Discuss DIY. Hi Is a 2.5mm T+E cable ok for kitchen appliances ? in the UK Electrical Forum area at ElectriciansForums.net

Redmist

DIY
Reaction score
0
Hi My new extension has 2.5mm T+E cable running to the Hob. The hob needs replacing I have been advised that there should have been a minimum of 4mm cable running to the Hob to comply with part P of the building regs ?
Could you please clarify this for me.
many thanks
Wojtek
 
T&E should not be used in this case. Heat resistant flex would be my choice. Cross sectional area of the cable depends of the rating of the hob and circuit protective device.
 
Is the T&E connected directly to the hob?

What circuit is the hob powered from sockets or on it's own circuit and do you know the MCB size for the circuit?

What's the rating of the hob?
 
Many thanks for your reply'
The hob is a Zanussi Induction hob 13 Amp supply.
it has its own circuit.
not sure about the other things.
Then on the face of it that's fine for the supply to the hob isolator. Most 13a appliances come already flexed, so I'm assuming that's the case here and the flex goes to the isolator. Or are you saying this is 2.5 T&E also.
Whatever, no need for 4mm, and it has nothing to do with part p.
 
So you have 2.5mm2 t&e from consumer unit to the socket where hob is plug in. All good providing your replacement hob will have the same rating of 13A
 

Reply to DIY. Hi Is a 2.5mm T+E cable ok for kitchen appliances ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
508
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
477
Seen a couple of videos with Doncaster cables now producuing a T&E with the CPC already sleeved so no need to fit our own. I also read somewhere...
Replies
19
Views
884
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
925
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
668

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock