Could someone explain how using a 3 wire tester would give a different result for Ze. I have a 3 wire tester but only use 3 wires when I don't want to trip the RCD, if I'm measuring Ze I just use 2 wires.

It is possible to get different readings by changing from a 2 wire to a 3 wire test on Ze or Zs.


Example from a real fault, (Megger 1552)
Tested a socket for Zs with plug, got a reading of 2.8ohm, tested another socket, 2.7ohm, maybe a broken ring or something? But continuity and readings OK on ring.

Go to another ring, high readings there as well.

Maybe Ze is high, so I did a two wire 20A bond test at the board, got a reading of .2ohm ish.

Strange I thought, get 2 wire Megger 345 no trip out, and do Z tests across the board all low readings?


Turn board off, do ohm test across MCB's check other circuits all OK?


Test across Neutral contact of double pole RCD and get 2 ohms ish FFS


Three wire testing uses the neutral as well.



Also on Hager RCDs and MCBs, always test for contact resistance they they burn easy, I have had around 5 cases of this.


Hope this helps.
 
On a Ze you should be testing L-N anyway!Really? I have installed hundreds and hundreds of Hager boards and never had or heard of anyone having a burned out main switch or breaker.Had a couple dodgy rcd's and that's it!You must be buying fake stuff
 
ombusdman are sill to get back to me about S.P.s extorsionate charge for fitting an isolator as they dont cut and reseal any more only fit isolators at £150 ffs I told them Id pay no more than £50 as 1 hr and £15 for isolator but they have monopoly
 

Reply to DNO Issue !!!! in the Australia area at ElectriciansForums.net

Similar Threads

On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hello there. I've been looking around here and found some conflicting information. I have a question if I may ask. I had an electrician come over...
Replies
30
Views
4K
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
644

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock