Engineer54
What's testing a socket got to do with he's supply Ze?? All he would be seeing is Zs, that maybe acceptably low due to good earth paths from the Gas and Water bonds.
that wasn't an engineer, that was a monkey. like measuring the titanic's funnel, then saying the ship was OK.i ad something like this ze high they sent an engineer around tested one double socket got an acceptable reading and left
As tony says if they provide an earth then they are under a legal obligation to maintain it. If they did not provide one or some cowboy has put an EC14 earth clamp around the paper lead incoming cable they will charge to supply a PME earth terminal.
OP why is it not ok for the DNO to use 2 wire testers??? When testing Ze they should remove the cutout fuse and customers earth and test L-N on concentric pvc supplies (PME, TN-C-S) and L-N and L-E on paper lead cables TN-S and (PME, TN-C-S). You do not need three wires to do this!
Could someone explain how using a 3 wire tester would give a different result for Ze. I have a 3 wire tester but only use 3 wires when I don't want to trip the RCD, if I'm measuring Ze I just use 2 wires.