The C Tec system I wired just used 2 cores for smoke,heat or sounder bases,but some expert will be along soon to explain your system.Hi,
Im wiring a fire alarm system and I was going to use the sounder bases as opposed to stand alone sounders.
Can the sounder bases be wired within the zone circuits or do they still need a sounder circuit wiring as well as the smoke heads?
it’s an ESP Mag fire system.
thanks
That’s great. Thanks a lot!The ESP mag fire panel is conventional so it will require the sounders and field devices to be on separate circuits