so, to sum up. if there's a window , not letting in enough light to see the fan, you don;t need an isolator. if the client has cfl lighting , you need an isolator, even though you still can;t see it with the lights on. all boils down to the good old torch. think we all know how to use one
 
no. a like for like replacement does not have to have circuits upgraded to latest regs, e.g. RCD protection provided. if you fitted an isolator, you'd have to provide RCD protection to the circuit if not already there.
 
Thanks for that, that's what I thought, someone wants a couple replaced and I'm sat here with BS7671 and building regs book trying to decipher it, cheers
 
basically, if you modify a circuit, then that circuit in it's entirity has to comply with current regs. including checking/rectifying earthing/bonding but just changing an accessory does not modify the circuit.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
Does the fan isolator in a bathroom have to be on the outside wall?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
atm-12,
Last reply from
telectrix,
Replies
20
Views
69,363

Advert

Back
Top