D danpic Jan 28, 2013 #1 Would a 16 amp MCB be capable for a kitchen ring?? 3x double plugs, 4x 13 amp fuse spurs for the washing machine etc.. and the cooker is on its own mcb...thanks
A accordfire Jan 28, 2013 #2 Erm...no, if it's a ring final.... And probably no for load too. Upvote 0
P pete555 Jan 28, 2013 #4 not quite but it can be a 16amp mcb providing it is a 17th split db with rcd,s on but i think overload could be a problem Upvote 0
D dan86 Jan 28, 2013 #6 I would say no. you say 3x double plugs, but depends what you'll be plugging into them. probably overload. Upvote 0
C currie123 Jan 28, 2013 #7 No not really suitable 2-3 appliances on at once And you will overload the circuit Upvote 0
C chrish_1977 Jan 28, 2013 #9 Don't want to sound like I'm being mean, but do you have any experience as an electrician? Upvote 0
4 44ALLAN Jan 28, 2013 #10 Why would you want to put 16 amp on a ring main mate? Washing machine and tumbler takes you to that !!! Upvote 0
D danpic Jan 28, 2013 #13 ive not done it yet...its the only mcb left. ill go and purchase a 32 Upvote 0
ETradesmen ~ Jan 28, 2013 #14 In terms of circuit design 16amp is not enough to supply ALL of the electric points you have stated. The most you will get is a 2x 20amp radial circuits (split the ring in two) lets hope they don't make a tea whilst doing the laundry Michael Upvote 0