G
GLENNSPARK
you IR between neutrals on finals......and that certainly would show up anything shared.....Yes I carried out what I thought to be all the neccessary checks, basically running through the schedule of test results sheet.
ZE, PFC at DB. Earthing type, Continuity, then IR on induvidual circuits.
I thought this was all that was required before a cu change...
sorry if this is frustrating for you guys, but I can't see how a global IR test would indicate that there is a problem between two neutrals as the neutal bar and earth bars are left untouched arent they?
thats why we do it....
its common on older installs.....