Originally Posted by Engineer54
Trying the RCBO approach as an initial fix, is probably the best way to go!!

I would do this anyway, to prevent the shower from tripping most of the installation out, in the event of a fault (just like this one).

Also to provide some load balancing at the CU, as the shower is on the same side as the cooker and RFC's at the moment, there are only lighting circuits on the other side of the board.
 
well i`m sorry eng ..but as someone who looks on RCDs somewhat dubiously...i find this post strange.....


Nothing wrong with RCD's mate, .....When there working!!

It's when they don't, and your totally relying on them for your earth fault protection, you need to start worrying...lol!!!
 
Almost certainly leakage from element(s) to heater tank. A hot element-tank IR test should confirm this. Replace the heater tank or complete shower unit. Once an element starts to breakdown it will only get progressively worse.
 
Thank You very much to everyone that has provided assistance regarding this matter. I'm pleased that it seems my line of thought is correct.

1SC
 
Clamped my earth leakage meter onto the shower circuit cpc and obtained very high readings, high as in exceeding 30mA high on one instance.
Coming to this one a bit late, I know, but if you can get your current clamp around both the line and neutral supplying the shower, set to the mA range, you will see exactly the same differential current from that circuit that the RCB sees. This should be a more accurate picture of the situation than just clamping the cpc (although it's a good start) which can be affected by parallel earth paths through pipework.
 
Thanks for your input HandySparks. I will have to try this method on the next opportunity:thumbsup

Received an update this afternoon. No tripping since shower circuit has been isolated :)
 
Thanks for your input HandySparks. I will have to try this method on the next opportunity:thumbsup

Received an update this afternoon. No tripping since shower circuit has been isolated :)
yes because the difference between the 2 is the imballance that the RCD senses.....and a ramp test will tell you at what point it lets go....giving you a max value difference before it lets go.....
 
but dont forget that accumilated earth leakage will play a part here so you could ramp the RCD...with all final circuits/connected loads fed by that RCD on......that will take into account accumilated earth leakage the higher they are...the lower your ramp should be
 