Im lost again an out building with loads of halers.

Is it the out building that has the Rod or the main Earthing arrangements for the premises as you say the reading for the TNS was too high!!
 
Being stupid, as their was no main earth bonds connected thought it would be ok.

Have not been able to test inside the house yet as owner are away till next week, but i have had major issues with DNO lately and Ze being too high and they will not do anything about it as they say they do not maintain the earth?
 
Im lost again an out building with loads of halers.

Is it the out building that has the Rod or the main Earthing arrangements for the premises as you say the reading for the TNS was too high!!
can get like a roundabout these....lol....
 
Ok sorry only referring to outbuilding.
The Ze of outbuilding if i use the TNS supply is 1.48. If i use the earth rod we put in then the Ze is 11.1
 
because if it is and the DNOs equipment is already being used as the means of earthing to this property ..clearly it is (TN-S)....then they have a duty of care to maintain this arrangement......
 
OP said couldn't get access so i'm thinking no, which could be the reason for his high Ze value.
 
Have not tested the Ze of the main house where the Ze supply comes from as owners are away till next week.
 
because if it is and the DNOs equipment is already being used as the means of earthing to this property ..clearly it is (TN-S)....then they have a duty of care to maintain this arrangement......

I have had 2 flats i tested in london in the past 2 months where DNO will not sort out high Ze. Has been a nightmare!
 