Hi I am new to the forum and looking for some advice.

I was supposed to have a vehicle to grid car charger installed last week. But they couldnt get a suitable earth from the earth rod. The earth rod reasing was 384 ohms. They're saying I need a marconite pit. the reading has to be below 100 ohms. Do i have any other options? I cannot use a matt:e box.

Would driving the rods deeper get it under 100 oms? a 8ft or 12ft rod? Or do I need a bentonite or marconite pit?

Any help appreciated.
 
Use a Zappi charger and/or get someone qualified to install one. No issue with earth rods then. The cost of the proposed works will most probably be more than the extra for a Zappi!
 
I want to use the Vehicle to grid charger instead of a zappi charger. The V2G charger needs a earth rod. They have said they don’t have someone in my area who can install the earth rod. That’s why I’m asking for advice.
 
Hi - I wouldn’t be too happy with that rod for use at my home and I’d be looking to understand 5e reading and improve it if possible. It might be a corroded connection for example (?). If you’d like some help with investigating and putting in more rods I’m sure someone here would be able to help you.
 
Is the earth rod you are talking about an existing setup for your home, or one put in specially for the charger?

As Wilko says, its not very good as the IET guidance says above 200 ohm is suspect.

It could be a badly corroded copper clad rod (not likely if solid copper/brass of course) or you have very dry soil (unlikely recently!) or something strange is happening.

If it is due to the soil type, etc, then you can go deeper or put in more than one rod suitably spaced. Neither are linear (i.e. you need roughly 2.5 times rod length for half resistance) but are easy option.

Finally if putting in a new rod, or much longer one, check for pipes or cables first!!!

Background info for the interested (or bored):

If looking for (major) utility pipes, etc:
 
Where did he try fitting it, and any idea of what sort of soil conditions are there?

Bentonite clay is often used to help earthing rods:


We had a quote a while ago for something like £13 for 25kg bag, no postage mind! Still needs a source of moisture though, it works by keeping that close to rod I think.
 
What sort of soil do you have there? (sandy/gravel/clay etc)

Did he try installing the rod close to the building foundations?

Is your driveway fully paved or is there either grass or a flower bed close by where you can dig?

Rather than a rod you could lay tape in a trench or use conductive concrete (Marconite based). Conductive concrete isn't cheap at around £100 for a 25kg bag.

EV charger installation companies tend to have quite narrow profit margins and will not want to be messing around trying to get a good reading when they could be making money installing another unit somewhere else.
 
Forget installing a rod and messing about with Marconite etc. Install one of these between the fuse board and charger. I install them on a lot of chargers in Somerset now as ground conditions or location make a rod not realistic. Simply route the supply through this box and you are good to go.
With the next generation of chargers and the current higher end models of chargers you can use PME and not have to worry about earth rods. more and more will go down this route as they update the model range.
 
Forget installing a rod and messing about with Marconite etc. Install one of these between the fuse board and charger. I install them on a lot of chargers in Somerset now as ground conditions or location make a rod not realistic. Simply route the supply through this box and you are good to go.
With the next generation of chargers and the current higher end models of chargers you can use PME and not have to worry about earth rods. more and more will go down this route as they update the model range.

Is that one of those mythical box's of tricks, JW & E5 Group talks about :)

 
Last edited:
Forget installing a rod and messing about with Marconite etc. Install one of these between the fuse board and charger. I install them on a lot of chargers in Somerset now as ground conditions or location make a rod not realistic. Simply route the supply through this box and you are good to go.
With the next generation of chargers and the current higher end models of chargers you can use PME and not have to worry about earth rods. more and more will go down this route as they update the model range.

I cannot use a Matt:e box with the V2g charger. If it was a pod point or zappi i could.
 
I cannot use a Matt:e box with the V2g charger. If it was a pod point or zappi i could.
How come? Be interested to know the reason?
[automerge]1584554274[/automerge]
Is that one of those mythical box's of tricks, JW & E5 Group talks about :)

Yes, there are some 'concerns' about them but arguably no more so than exporting PME outside the zone. The regs permit it and the manufacturers now include it in some chargers.
 
How come? Be interested to know the reason?
[automerge]1584554274[/automerge]

Yes, there are some 'concerns' about them but arguably no more so than exporting PME outside the zone. The regs permit it and the manufacturers now include it in some chargers.
Least if the rod is installed to specification, it will work as designed. Seems we are relying on manufacturers for these devices to work, with no way of knowing if they do.

Have you been sold a pup?
 
Yes, there are some 'concerns' about them but arguably no more so than exporting PME outside the zone. The regs permit it and the manufacturers now include it in some chargers.

Is that not the main concern? The exporting PME under fault conditions is dangerous for something like a car that is bound to be touched.

Looking at those boxes it appears they are designed to isolate if the voltages look wrong as whatever amendment 1 will allow (no sign of any CT), but that is not a very reliable test without access to true earth (even high Z) or similar.

It might see hearsay, but using a 3-pole RCD (or ye olde ELCB design that actually measured earth current) to check for "external" earth current as well and so isolate the car completely (L, N & E) would make a lot more sense.
 
You are not exporting PME, PME stops at the source of supply. You are using a cpc which happens to be connected to a PME system. And what is this Zone you are exporting it out of?

Yes, your are correct in terminology.

The issue is the CPC could go to well over 50V under fault conditions (open CNE, imbalanced 3 phase load) and a car is located in a zone close to "true earth", which is exactly the situation that the IET guidance for caravans was designed to protect against.

For them it recommends a local TT supply (separate rod and 2-pole RCD). But a fancy RCD could cover all three conductors (L, N, E) but look for specific currents:

|L-N| > 30mA
|E| > 30mA

Neither should be present, but if any are they are then disconnect all 3. An L-E fault would show on both tests, a PME fault would show as E but only if someone touched the car, etc.

OK, you no longer have earth bonding after a disconnect and I guess that might be an issue of there is an alternative source of power, but it would cover both the EV and caravan cases.
 
Poor terminology on my part.
I dont necessarily agree with these devices, A company I sub contract for now insist on them , especially in the inner city installs or where bedrock makes the installation of a rod a non starter.
I accept they have limitations, not least on some of them a simulated or calculated reference to earth rather than a true measurement. its a big assumption to make in worse case scenarios. but the manufacturers stand by there product. AMD1 has permitted them.
 
No sorry it isnt a current earth rod. The electritian, from the car charger company, tried to install an earth rod but got a earth reading of 384 ohms so he removed it.

How long was the rod? I assume there was only one?

If it was a single 1.2m/4' rod then there is not much chance of it ever achieving a suitable low reisistance to earth.

Personally as a bare minimum for an earth rod installation I would start with 2x 2.4m/8' spaced ideally 5m+ apart and then measure the resistance to establish what further work is necessary.

A single short rod, even if it is suitable initially, is unlikely to maintain a stable resistance to earth throughout the seasons.
 
How long was the rod? I assume there was only one?

If it was a single 1.2m/4' rod then there is not much chance of it ever achieving a suitable low reisistance to earth.

Personally as a bare minimum for an earth rod installation I would start with 2x 2.4m/8' spaced ideally 5m+ apart and then measure the resistance to establish what further work is necessary.

A single short rod, even if it is suitable initially, is unlikely to maintain a stable resistance to earth throughout the seasons.
I'm guessing not that long if he's managed to remove it. Used to have a hell of a job removing temporary electrodes when knocking down sites.
 

Reply to Earthing a V2G Electric Car Charger with a earth rod in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I’m after some advice for an existing car charger that’s on one of our newly inherited sites. We have a Rolec 2x 7.2kw pedestal charger, just...
Replies
0
Views
1K
Qualified electrician has installed Zappi car charger outside house. Grid incoming goes to DNO cutout then to SPD then to meter then to henley...
Replies
21
Views
5K
Hi Thanks for providing the forum... Wonder if anyone here knows the regs on the installation of a 7Kw car charger, in so far as where it can be...
Replies
2
Views
2K
Evening all, Just After some knowledge about the Matt:e. I have been to a job where a 13 amp Rolec car charger point has been fitted On an...
Replies
3
Views
2K
Following on from another thread I have some more pictures and some more information. There are 2 questions in bold. The customer has bought the...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock