B
Bazultra
Hi ive just started to test installs on a regular basis again and am not 100% sure when to enter EEBADS or ADS in the protective measure(s) box. Also would the ADS time be different depending on the earthing arrangement TNCS,TNS or TT etc?
Thanks Baz
Dont see the point of even having the box if all installs are ADS. Also what would the disconnection times be for a TNCS system 0.4? Also no I am about to do the 17th amongst other things. A bit stale at the moment. Thanks for your help fellow sparks:)
you still have automatic disconnection of the supply - but supplementary equipotential bonding can be omitted if there is rcd protection.
..........you still need main bonding to the gas and water.
I just read through that markc123 but am still confused as it only has the values for TT and TN system not TNCS or TNS
Acording to NICEIC inspector, this weeks visit, generally anything below 32amp is 0.4 sec.
I done it wrong, 0.4 for sockets and 5 sec for ltg and supplies to heaters etc. (all non domestic )
Boydy
Surely if the installation was installed pre-17th edition with all the bonding, it would still be EEBADS because in certain cases it can rely on the bonding for disconnection?
I thought the idea behind an rcd was to disconnect due to some of the electric escaping somewhere (ie to earth).
EEBADS or ADS
Thread Tags
Tags Tags
None
Bazultra,
Adam W,