Hi,

Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two separate circuits. The SWA has the Brown on a 10A MCB and the Grey is on a 16A. So clearly they have shared earths and shared neutrals, similar scenario with SY. What code fault would you put this down as?
 
Have they definately got a shared neutral between the 2 circuits on the SWA?
Normally when using a 4 core SWA for 2 circuits there would be 2 lives, 2 neutrals and a shared CPC (the armour) which is fully compliant.

However with a 4 core SY (assuming that is 4 cores total not 4 cores plus earth) that is obviously not possible.
If they have used a shared neutral between 2 circuits I would code it C2.
They may alternatively have connected the cores as seperate neutrals and used the braid as a CPC which is also unacceptable and would attract a C2 code.
 
With the SWA being on two separate phases and different size MCB’s surely that can’t be compliant. We haven’t traced the cable as of yet but presume it goes to a Joint Box.
 
With the SWA being on two separate phases and different size MCB’s surely that can’t be compliant. We haven’t traced the cable as of yet but presume it goes to a Joint Box.
If it has a 'borrowed neutral' (common N to the two circuits) then it is C2 no matter what, as above.

It should be labelled as having more than one point of disconnection at either end.

Otherwise it is not elegant, but you see multiple singles in conduit doing much the same idea.
 
It should be labelled as having more than one point of disconnection at either end.

I don't think there's any requirement for a cable carrying multiple circuits to be labelled as such, only equipment which cannot be isolated from a single device.

Otherwise it is not elegant, but you see multiple singles in conduit doing much the same idea.

It can be an elegant soloution. Working in theatre/stage lighting circuits are usually in multiples of 6 so it is quite normal to use muticore SWA to carry multiple circuits to the same place.
 
I would go with an FI until you can put sufficient resources to identifying the conductors and feed arrangements for the circuits. This will have the same end result as a C2 and would give an unsatisfactory EICR. You could add into this "Unsatisfactory pending further investigation of circuit wiring for circuits X"
 
Hi,

Currently undertaking an EICR on a factory, we have came across an 4 core SWA and 4 Core SY which have been split in the DB to serve two separate circuits. The SWA has the Brown on a 10A MCB and the Grey is on a 16A. So clearly they have shared earths and shared neutrals, similar scenario with SY. What code fault would you put this down as?
You need to identify what the situation is before you can apply the correct code (if one is required at all), else your report maybe inaccurate, if not it may require further investigation. Is your statement (my bold) an assumption or verified as true?

As westward10 stated - "Providing the circuits are electrically separate including the neutral conductors and the insulation of the conductors is rated for the highest voltage then it is fine".
 
I would go with an FI until you can put sufficient resources to identifying the conductors and feed arrangements for the circuits. This will have the same end result as a C2 and would give an unsatisfactory EICR. You could add into this "Unsatisfactory pending further investigation of circuit wiring for circuits X"

There's nothing to be investigated.

FI is not the same as a C2 and it doesn't give the same result.
 
I think what Lister is getting at is that the OP hasn't confirmed if the neutral is shared between the 2 circuits. That's what needs further checking.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Carlisle
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
EICR Code for two circuits on one cable.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
Slewis120,
Last reply from
DPG,
Replies
14
Views
4,631

Advert

Back
Top