Earth rod measures 247 ohm, with water and gas connected 233ohm. All covered by 30maain rcd.
C3? Improve the rod reading to below 200?
And if or when the RCD device fails to operate, will 199 ohms be tickety boo??
Unstable so a c3 IMOEarth rod measures 247 ohm, with water and gas connected 233ohm. All covered by 30maain rcd.
I can see your point, and wouldn't consider it a mistake if no code was given, I would suggest a 3 due to the fact it is over the 200 and could be considered unstable and need to be watched or investigated further, a no code is understandable and I think many others will agree with you.No code, I'd note it and recommend the customer allow at least a quaterly Ra reading to be taken to further determine it's stability. Another recommendation would be to fit an s-type up front.
Tin hat firmly strapped on!!!
That is the reading which will allow the RCD rated at 30ma to trip, we work to the regs regarding RA values, 1667 is not in the regs, your whole post is totally wrong I am afraid.The 200 ohms figure is only advisory to allow for freezing or drying out , what were the conditions when you tested ?, the regs only require that the resistance meets the criteria for a given RCD and protective requirement, if you take 30mA for additional protection then thats 1667 or the same device for fault protection its 7667 ohms, and for a 100mA 2300 ohms
yes that is the maximum ohm rating to allow a 30ma trip to work in the required disconnection time, we all know that. It is not the maximum allowed RA on a TT system is it, jeezTable 41.5 page 57.