I simply tell the customer they are paying for a report, as I find it. I leave it fully confident that they can get another sparky in if they wish to verify any faults I have highlighted.
 
I fitted 3 lengths of 2.5mm butyl flex to immersion heaters yesterday. I'll let myself off over sizing the cable though as they were 4kW elements. Now that would have been pushing 1.5mm flex to its limit, but a 3kW element certainly wouldn't.
 
I don't see how you can consider that to be running it close? It is only 4/5 of the rated current of the cable

Indeed. For anyone worried about using a cable near rating, remember that the heat dissipated is proportional to the square of the current, in this case 16/25 or about 64% of the permitted temperature rise.

I can see the point in standardising on 2.5 for 3kW aircon loads though as the voltage drop during compressor starting is critical and might often be a more onerous requirement than CCC.
 
Indeed. For anyone worried about using a cable near rating, remember that the heat dissipated is proportional to the square of the current, in this case 16/25 or about 64% of the permitted temperature rise.

Please can you explain this one to me as I've not heard / been taught this calculation / consideration .... sorry if I'm being dumb!

p.s.Can we not just say heat resistant flex rather than butyl ... its so much easier to spell!!:tounge_smile:
 
Please can you explain this one to me as I've not heard / been taught this calculation / consideration .... sorry if I'm being dumb!

p.s.Can we not just say heat resistant flex rather than butyl ... its so much easier to spell!!:tounge_smile:

Butyl has enhanced heat resistance over standard duty flex, but not all heat resistant flex is butyl. Butyl is rubber HR flex but you can get PVC HR flex too.
 
Please can you explain this one to me

P=I²R

This P being the one dissipated in the cable, not the load.
 
Cheers.

I now need to learn to spell butyl correctly then! Lol! Only every used "heat resistant flex" from wholesalers. I'll have a look into when butyl would be prudent in comparison to heat res. flex.

I didn't notice the link between P = I2 x R, so thanks for clarifying for me
 

Reply to EICR on a Sunday in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just your thinking on this… Doing Remedials on a EICR … the DB is a old Wylex with MCB”S/RCD Its a 10 way… rammed packed with cabling,,,the...
Replies
3
Views
1K
I went out today to carry out an EICR on a domestic property. The lead up to the job had been confusing. The elderly (roughly @telectrix 's age)...
Replies
10
Views
2K
I've done a few EICRs for a landlord and the latest one of his I've given an unsatisfactory, I've advised changing the CU - existing one is old...
Replies
18
Views
2K
I wonder if anyone has some good stories of really easy call-outs made a lot more difficult by the customer's rather fixed views. Here is my...
Replies
39
Views
5K
Hi. I thought I would introduce myself on here in the hope to gain some valuable information on setting out on my own. I'm 42 and have been an...
Replies
116
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock