I simply tell the customer they are paying for a report, as I find it. I leave it fully confident that they can get another sparky in if they wish to verify any faults I have highlighted.
I don't see how you can consider that to be running it close? It is only 4/5 of the rated current of the cable
Indeed. For anyone worried about using a cable near rating, remember that the heat dissipated is proportional to the square of the current, in this case 16/25 or about 64% of the permitted temperature rise.
Please can you explain this one to me as I've not heard / been taught this calculation / consideration .... sorry if I'm being dumb!
p.s.Can we not just say heat resistant flex rather than butyl ... its so much easier to spell!!:tounge_smile:
Please can you explain this one to me