Discuss EICR question - gas bond off main TNS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I think I'd be getting the DNO in to sort that 951 clamp on the incomer and possibly the service head as it looks like it may be fused on the neutral as well as the live
I think I'd be getting the DNO in to sort that 951 clamp on the incomer and possibly the service head as it looks like it may be fused on the neutral as well as the live on
ok thank you.. is this the way they used to do it? It’s seems to be a cut out I’ve never seen before? Would you Earth it from gas clamp straight to CCU instead?
At some point it is possible the main earth terminal has been removed for whatever reason, hard to know who fitted the 951 clamp on the incomer but that may be when the MET was removed
It would probably be better to take the bonding to the CU although I would be careful messing around with the 951 clamp on the incomer in case you damage the cable and it may be better to speak to the DNO before doing anything
Reply to EICR question - gas bond off main TNS in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...