Just a quick one. Testing a house that's install is about 20 year old. Obviously hasn't got a metal clad DB, earthing is only 10mm. Would you put these down in the reccomendations? Even though these items were perfectly fine when it was installed?
Lee
 
Just a quick one. Testing a house that's install is about 20 year old. Obviously hasn't got a metal clad DB, earthing is only 10mm. Would you put these down in the reccomendations? Even though these items were perfectly fine when it was installed?
Lee
What size are the L/N tails?
 
I'm with Murdoch - TNS or TT and that 10mm is probably more than adequate. I recently installed a 10mm on a rewire because it was a tricky run and 16mm would have made it much harder to pull. Adiabatic only needed a 4mm, so 10mm more than enough.
 