Discuss Eicr - who can do remedial work in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
22
Firm we work for uses a national testing / safety firm for all health and safety etc.
They have carried out a eicr and there is a few c2, and 1 x db change / further investigation noted.
They say only they can carry out the work at extortionate prices.

How do we stand.
Do we do work and issue a eic for the work done. And add this to paper work they gave, but cert is unsatisfactory.
With a covering letter stating work done.
Before anyone says I've not got 2391 testing cert, but can carry out installation work.
Thanks.
 
You don’t need to use them to carry out the remedial works, you can employ any spark you see fit to do that.

If you’re competent to do the installation work and issue a cert yourself then there’s no problem doing that either.
[automerge]1596750280[/automerge]
You don’t need to use them to carry out the remedial works, you can employ any spark you see fit to do that.

If you’re competent to do the installation work and issue a cert yourself then there’s no problem doing that either.


Forgot to say, you may have an unsatisfactory certificate, but it will have a date on it recommending when the next test should be carried out “as long as all remedial works have been rectified”

So as long as you can prove they’ve been carried out, you’ll be good to go until the next test date.
 
Anyone can carry out the remedial work.

I always advise that different contractors should carry out the EICR and the remedial work to avoid false reporting and cowboy tactics such as you have experienced here.
Hi
Presume we just carry out work and put a covering letter with eic stating what we've done.
Yes they are basically ringing up every other say stating they need to do work
 
Hi
Presume we just carry out work and put a covering letter with eic stating what we've done.
Yes they are basically ringing up every other say stating they need to do work

Tell them that you will be getting another contractor to do the remedial work and if they continue to harass you then you will report them to trading standards for using these bullying tactics.
 
Tell them that you will be getting another contractor to do the remedial work and if they continue to harass you then you will report them to trading standards for using these bullying tactics.
or report them to their scheme. i hear that NICEIC are running short of toilet paper ( coz. that's all NICEIC will use your report for ).

seriously though, as above, do the remedials, attach a EIC to the EICR. all good.
 
Before anyone says I've not got 2391 testing cert, but can carry out installation work.
Thanks.
The crazy thing is that, for EICRs, there are no qualifications required to carry one out (thats partly why we see things like this).
Also, no quals are needed for remedials, unless the remedial extends to notifiable work, like a replacement consumer unit.
 
The crazy thing is that, for EICRs, there are no qualifications required to carry one out (thats partly why we see things like this).
Also, no quals are needed for remedials, unless the remedial extends to notifiable work, like a replacement consumer unit.

Wait. Anyone can carry out an EICR, without having attained any sort of qualification in inspection and testing?

That's a bit daft.
 
Wait. Anyone can carry out an EICR, without having attained any sort of qualification in inspection and testing?

That's a bit daft.

That’s correct, you only need to be competent, although a lot of schemes will ask for a qualification in inspection and testing if you want to carry them out under their banner; and a 2391 qual goes a long way to proving competence with them.
 
That’s correct, you only need to be competent, although a lot of schemes will ask for a qualification in inspection and testing if you want to carry them out under their banner; and a 2391 qual goes a long way to proving competence with them.

I don't know the whole ins and outs of the industry, but had laboured (incorrectly) under the assumption that 2391 was required for anyone who carried out testing and ispection of installations.
 
I don't know the whole ins and outs of the industry, but had laboured (incorrectly) under the assumption that 2391 was required for anyone who carried out testing and ispection of installations.

If that was the case I'd have a legitimate reason to get out of doing EICRs, I don't have any inspection and testing qualifications.
 
And I guess many people who are in receipt of a 2391 qualification might struggle with some of the weird and wonderful stuff you find during those EICRs.


True, regardless of what qualifications you hold, something can always pop up that you’re unsure of; and being able to draw off other people’s experience is a blessing when it does.
 
Back in the day, when I signed up with NAPIT, 2391 was mandatory. Understandable considering what the NAPIT initials stand for. Then along came Part Pee and a gravy train for organisations like NAPIT who turned themselves into an expensive installers register.
What has evolved is that you can be a member of a CPS with little more than 5-day course and access to £600. If you are a CPS member, they will want you to have a T&I qualification (2391 or whatever the dumbed down version is called now) if you are going to do EICRs under their umbrella. Quite right too.

However, someone who is not a CPS member With no qualifications of any sort, and only scant understanding of anything, can carry out EICRs, wrongly condemning perfectly serviceable installations, costing householders and landlords unnecessary expense.
Crazy.
 
Back in the day, when I signed up with NAPIT, 2391 was mandatory. Understandable considering what the NAPIT initials stand for. Then along came Part Pee and a gravy train for organisations like NAPIT who turned themselves into an expensive installers register.
What has evolved is that you can be a member of a CPS with little more than 5-day course and access to £600. If you are a CPS member, they will want you to have a T&I qualification (2391 or whatever the dumbed down version is called now) if you are going to do EICRs under their umbrella. Quite right too.

However, someone who is not a CPS member With no qualifications of any sort, and only scant understanding of anything, can carry out EICRs, wrongly condemning perfectly serviceable installations, costing householders and landlords unnecessary expense.
Crazy.

In an ideal world, people would only take on jobs that they were confident about and which fell within the scope of their abilities. Unfortunately this isn't an ideal world and there will always be people ready to grab any opportunity that comes along, if it means they can pocket a few more pounds.
 
In an ideal world, people would only take on jobs that they were confident about and which fell within the scope of their abilities.
Alas, we also have this to contend with:
You don't need to read the Wiki article, as the title of the original academic paper (Kruger and Dunning, 1999) says it all:

"Unskilled and Unaware of It: How Difficulties in Recognizing One's Own Incompetence Lead to Inflated Self-Assessments"

Having recognised qualifications is a good route to doing the related work, but they don't always mean a person is that competent, and there are folks out there (in this forum, for example) who lack the formal qualifications but could teach actually the course if needed!
 
An interesting point raised here, the new landlord laws it seems call for a level 3 qualification, but the BS7671 only says must have the skill it does not require any paper qualification, and it seems it is up to the owner to verify the person doing the EICR has the qualifications and insurance required by law.

I had the same with LABC when we kicked off the guys doing a conversion toilet and pantry into a wet room, I had assumed (incorrectly) the builder had informed LABC so I told them I was taking over the job, and we were told off for starting before they said go, and also told in no uncertain terms it was the home owners job to tell LABC if the builder did it then that was a service he was providing, but it was our job to verify he had.

Unlike a new installation there is no requirement in England and Wales not sure about Scotland, to be a member of a scheme to do an EICR. And it would seem any level 3 remotely connected to electrical work will do, we would hope for C&G 2391 but it would seem my radio amateurs exam (RAE) would fit the criteria, which since the exam was stopped around 25 years ago clearly anything learnt would be well out of date, think the Scottish rules do have a clause about resent learning.

Until we left the EU we were obliged to accept qualifications from other countries, so we are not just looking at City & Guilds. And even the 16th Edition was taught and tested by collages, with internal exams. This did cause problems with 17th Edition when students found they could not take the update, because their qualification was not registered with C&G.

Indenture's are still valid, and in my day one did not have to go to collage and take any exams to be considered qualified, once you finished your apprenticeship you were qualified, and my old qualifications did not have level 2 or level 3 marked on them, and an 'A' level is level 3.

And to be frank my level 5 qualification did not teach me anything about regulations, so even an electrical and electronic engineering degree does not help doing an EIRC although I do have my 2391 anyway.

When I wanted to buy a new house, I had a buyers report done, as part of the report it referred to the electrical installation and its condition, clearly the surveyor would hold better than level 3, and he would be insured, however although it was an EICR it was not to the standard expected for one done by an electrician.

So had I bought this house with the idea of renting it, I could have well considered I was covered, well since in Wales and the EICR is only required for multi occupancy I would be covered, but I am sure you can see my point, how can the owner know if the guy he has employed has the skill to do the inspection?

I noted on another forum how one electrician said he will only do one EICR per day as he must have the time to fix any small problems before he leaves, he charges for the day, and any parts fitted in the day only the price of parts is charged for, if he has to return only then does he charge for time.

But there is no requirement to have a clean EICR with no C2 items, all it needs is for the minor works to be included with the EICR, to show it has been corrected. However it seems letting agents don't follow the law, they often ask for well over what regulations and laws require. The regulations and C&G training state not potentially dangerous, but letting agents often it seems state all circuits RCD protected and metal consumer unit, clearly not required for a normal EICR but they still ask for it.

I came to consider letting out my mothers old house, and it had a domino hob, just two rings, letting agent was quite insistence they would not put the house on their books until changed, wanted four heating areas, so it is not restricted to the electrical installation they do ask for over and above what is absolutely necessary.

And to be frank that's no a bad thing, I want my house to be safe, and when I realised the type B written on the RCBO was actually type AC but curve B I ordered up two type A for the socket circuits. But on a risk assessment I decided not to change the other 12 RCBO's. As to if type AC RCD where inverter washing machines, and fridge freezers are installed should even get a C3 I am not sure? Would you list it?
 
But there is no requirement to have a clean EICR with no C2 items, all it needs is for the minor works to be included with the EICR, to show it has been corrected. However it
I was under the impression the new law requires all C2 "unsatisfactory" or FI to be fixed in 28 days?

And to be frank that's no a bad thing, I want my house to be safe, and when I realised the type B written on the RCBO was actually type AC but curve B I ordered up two type A for the socket circuits. But on a risk assessment I decided not to change the other 12 RCBO's. As to if type AC RCD where inverter washing machines, and fridge freezers are installed should even get a C3 I am not sure? Would you list it?
I think it is a marginal risk having AC type RCDs.

For personnel shock protection (e.g. drilling in to hidden cables, touching a damaged extension lead outdoors, etc) they will work just as well provided there is not enough DC fault to block them.

Yes, a faulty appliance might block them, but the bigger ones likely to do that should be earthed (and PAT tested to check that) so I suspect the majority of faults will still trip the RCD or at least take out the OCPD.
 
I was under the impression the new law requires all C2 "unsatisfactory" or FI to be fixed in 28 days?
Yes but only need to be fixed, you don't need a clean EICR you simply attach the Minor Works.

I see F1 as a problem, as to fix a F1 may not generate a minor works, so if for example a door was locked, if when open no fault found, then no minor works, but it seems even a bill for the work will do, so a bill for inspecting and testing living room no faults found would be enough.

So really the problem is where electricians miss code items, so if called to a home and the EICR says no RCD and when you get there it is clear it does not need a RCD, that is a real problem.

If some one with a C&G 2382 says in a report C2 no RCD and some one with a level 5 degree then says no RCD required, will that bill be good enough?
 

Reply to Eicr - who can do remedial work in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys, need a bit of advice, EICR was completed on the property which needed a new consumer unit and a few other bits like broken sockets and...
Replies
10
Views
810
So I've recently had an EICR for my building. Came back with about 20 odd C2 remedials and a few F1's which resulted in UNSATISFACTORY being...
Replies
5
Views
1K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
859
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock