P

Plonker 3

I have my Elecsa assessment booked in for the 6th of February my first one. For it I wish to do a DB change at my parents house, but there are a couple of problems I can see and wondered what would be the best solution for them.

1. Main bonding to the gas is currently just the other side of the wall from the DB, but there is a tee of it from the meter approximately 10 meters away which is also external.

2. The shower is 9.5 kw wired in 6mm, would this be fine just to put onto a 32amp RCBO or would I have to either change the shower or cable accordingly, also at present the shower has no local isolator and is mains fed direct would I have to amended this accordingly?

Any other things I should look out for also on my assessment?

Thank you in advance.
 
Ideally the main bonding should be before any tees and if it is an external connection then it should be straight forward to extend the main bonding along to the meter and before the tee.

For the shower you need to look at the current the shower is taking and the installation method of the cable.
You must meet the regulations required as regards the design current, CCC of the cable, and Ib<In<Iz.
 

Reply to Elecsa assesment in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
425
Hey guys and gals. We bought a small office trailer that is wired up. It's never seen mains power and uses a generator disconnect (220). I read...
Replies
0
Views
1K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
I have a customer with a farm who has a barn containing a large 3 phase generator which powers various equiptment at that location. A single...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock