Sonia Norman
Browsing to buy a new electric oven. I came across a Hotpoint with a rating of 10.7 kWh. I calculated that would need a 16mm cable! Surely not? I multiplied by 1.25 as when it's on its a continuous draw. Thoughts?
Diversity is your friend here.
From memory as not got my regs book to hand…
The first 10 amps + 30% of remaining load + 5 amps if your cooker isolator switch has got an integrated socket on it.
Have you applied the diversity formulae?Browsing to buy a new electric oven. I came across a Hotpoint with a rating of 10.7 kWh. I calculated that would need a 16mm cable! Surely not? I multiplied by 1.25 as when it's on its a continuous draw. Thoughts?
Just an oven, not a complete cooker, correct?Browsing to buy a new electric oven. I came across a Hotpoint with a rating of 10.7 kWh