Browsing to buy a new electric oven. I came across a Hotpoint with a rating of 10.7 kWh. I calculated that would need a 16mm cable! Surely not? I multiplied by 1.25 as when it's on its a continuous draw. Thoughts?
 
Diversity is your friend here.

From memory as not got my regs book to hand…

The first 10 amps + 30% of remaining load + 5 amps if your cooker isolator switch has got an integrated socket on it.
 
Diversity is your friend here.

From memory as not got my regs book to hand…

The first 10 amps + 30% of remaining load + 5 amps if your cooker isolator switch has got an integrated socket on it.

If my maths is right, it should draw just shy of 26 amps with diversity applied.

So depending on the length of run and installation reference method, it should be good on a 6mm cable and a 32amp MCB/RCBO
 
what he said. ^^^^^^^^. rare to find that you need to go up to 10mm cable. the 6.0mm cable is protected against overload by the 32A MCB. both cable and MCB will withstand 40% overrrating for up to 1 hour when the load exceeds 32Aif all elements are warming simultaneously ( woow, spelloing at 5.00a.m.after beer. I must getoutmore).
 
Browsing to buy a new electric oven. I came across a Hotpoint with a rating of 10.7 kWh
Just an oven, not a complete cooker, correct?
kWh (kilowatt hours) is a measure of energy usage. The electrical load rating (from which the current is calculated) is measured in kW (kilowatts). I don't think the oven uses 10.7kW unless it is a huge commercial thing, domestic ovens are typically no more than 4kW and many are less.

What is the actual rating in kW?
 
Last edited:

Reply to Electric oven cable size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
670
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
671
Hi all, I've recently had an oven installed by AO and afterwards I noticed in the installation instructions that the electrical connection needed...
Replies
1
Views
1K
I have just replaced my old double oven which was about 10 years old with a new model as whenever I used the top oven it tripped the electrics...
Replies
1
Views
605
Hi, I'm a first year apprentice... just trying to get an edge on theory. Calculating breaker size: W ÷ V = A So say appliance needs 4000 watts...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock