Search for tools and product advice,
Discuss Electric oven cable size in the UK Electrical Forum area at ElectriciansForums.net
Browsing to buy a new electric oven. I came across a Hotpoint with a rating of 10.7 kWh. I calculated that would need a 16mm cable! Surely not? I multiplied by 1.25 as when it's on its a continuous draw. Thoughts?
Diversity is your friend here.
From memory as not got my regs book to hand…
The first 10 amps + 30% of remaining load + 5 amps if your cooker isolator switch has got an integrated socket on it.
If my maths is right, it should draw just shy of 26 amps with diversity applied.
So depending on the length of run and installation reference method, it should be good on a 6mm cable and a 32amp MCB/RCBO
what he said. ^^^^^^^^. rare to find that you need to go up to 10mm cable. the 6.0mm cable is protected against overload by the 32A MCB. both cable and MCB will withstand 40% overrrating for up to 1 hour when the load exceeds 32Aif all elements are warming simultaneously ( woow, spelloing at 5.00a.m.after beer. I must getoutmore).
Just an oven, not a complete cooker, correct?
kWh (kilowatt hours) is a measure of energy usage. The electrical load rating (from which the current is calculated) is measured in kW (kilowatts). I don't think the oven uses 10.7kW unless it is a huge commercial thing, domestic ovens are typically no more than 4kW and many are less.
What is the actual rating in kW?
Reply to Electric oven cable size in the UK Electrical Forum area at ElectriciansForums.net
Hi, I am Currently in the process of building an extension and my builders will shortly be getting their electricians to commence the first fix...
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
I have just replaced my old double oven which was about 10 years old with a new model as whenever I used the top oven it tripped the electrics...
