Im not doing any work there tony, he just asked me if it would work, cheers engineer54, i'll let him know about the earth etc, hopefully talk him out of it! Thanks for your replies guys, clearly a big no no doing it this way but I was more interested in whether it would actually work this way. Whilst im on the subject what would happen if the main switch was left on and then the power returned from the suppliers source whilst genny was still running?
If someone working for the DNO got killed by power back feeding in to the grid, you’re mate would be most likely be on a manslaughter charge.
It is a constant problem with rural supplies when farmer Brown cranks up his generator. Without correct interconnection it back feeds through the local transformer and some poor schmuck gets 11KV up his arm.