Hallo there! I Have to install emergency lightimg in beauty salon, they will only go on in case of power failure, no overriding needed, can i use PVC t&e? Or it is a must for third cor? Thank you
 
third core only if your switching lamp/overriding ie. a maintained fitting with facility to switch lamp on/off for use while occupied perhaps. in short then no, just run permenant supply to them with a test point/s acsessable for testing and maintainance. as to the cable then all depends on the installation
 
You should make sure that FP isnt required, other than that T&E should be fine.
 

Reply to Emergency lighting, wiring. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock