There are various rooms, some rooms have one circuit, some rooms have 2 rings, all fed from various different DB's. Switching Db's is obviously not an option as offices etc are also supplied.

If i can find the rings coming into the rooms it will be a lot easier. It does look like a tidy install not too old, all labelled up so i would expect to see a tidy install above the ceiling as well, which will also help.
 
.... and use stop button to coil on N/C contractor ...

Do you really mean this "N/C"?

If so, I suggest that the job goes elsewhere.
 
With offices a various dbs now in equation ....this sounds like new circuits are required
Infinity ment N/C circuit Handy sparks
 
N/C circuit with switch opening the circuit what's wrong with this handyspark?

The circuits in the rooms do not supply figures just the DB's do hence no switching of DB.
 
Or as biff says change to radials....
 
You may also want certain sockets in the room to stay on even if the E stop is pressed E.g. computers around the room or a computer and projector on the front desk
 
N/C circuit with switch opening the circuit what's wrong with this handyspark?

Nothing.

But what you said was N/C contactor, ie closed when the coil is de-energised, which for an em-stop circuit is not what's required.
 
Work to the relevant & recognised Code Of Practice as published by the BSI, that is BS4163 and all will become clear, the requirements are spelt out in that standard, easy.
 
28 posts and only 2 give a descent reply
Mdj with the e stop and separate single key reset switch and blind Paul with the code of practice to go by.
 
28 posts and only 2 give a descent reply
Mdj with the e stop and separate single key reset switch and blind Paul with the code of practice to go by.

And your answer to multiply rooms with radials & rings mixed with offices, with numerous dbs located in different areas .....IS...?

Always one to make big comment.....without a solution.....!!!!
 
Last edited by a moderator:
  • Like
Reactions: 2 people
If I were faced with this (as described) I would:

1) Install submain DB to each lab incorporating contactor etc on din rail.
2) Get above ceilings and rewire/reroute all cabling as necessary to separate the labs/offices accordingly.
3) End result - each lab with own ring fed from new sub DB
4) E-Stop with keyswitch wherever.

A lot of work/cost etc but I don't see an alternative - just get stuck in!
 
  • Like
Reactions: 2 people
If I were faced with this (as described) I would:

1) Install submain DB to each lab incorporating contactor etc on din rail.
2) Get above ceilings and rewire/reroute all cabling as necessary to separate the labs/offices accordingly.
3) End result - each lab with own ring fed from new sub DB
4) E-Stop with keyswitch wherever.

A lot of work/cost etc but I don't see an alternative - just get stuck in!


Very similar to the requirements within our Medical Labs Building, except ours are a bit more involved, many being monitored by safety isolation supply units (similar to that found in many school lab classrooms), and a hazardous gas detection alarm system....
 
  • Like
Reactions: 1 person
Very similar to the requirements within our Medical Labs Building, except ours are a bit more involved, many being monitored by safety isolation supply units (similar to that found in many school lab classrooms), and a hazardous gas detection alarm system....

Not worked on that kind of setup - sounds interesting.

Strangest emergency stop install I've come across was in a number of MOD establishments where the stop button, when pushed, shorted neutral & earth on an RCD protected server installation (N+E picked up at nearest socket then wired to n/o on stop). I wasn't testing the install so thankfully did not have to code it lol.
 
  • Like
Reactions: 1 person
What he means monitored is by rcd .
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Emergency stops for LAB sockets
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
35

Advert

Thread statistics

Created
infinity,
Last reply from
Engineer54,
Replies
35
Views
9,212

Advert