hi, can't suss this, doing an extractor with run on timer, which has led light. Cabled the separate isolation switch, two way to fan, 2 way to jb, light switch l1 to isolator l1 at jb, sperate line feeds to lights, common to line at jb with live feed from lighting ring, neutral has neutral in and and out for lighting circuit, 2 lights out, neutral from isolator in. Test it and nothing on switching on, there is power in ok but both lights out and fan, nothing, can't see anything wrong with wiring, any suggestions other than give up and go for a pint!
 
Sorry if I'm reading your post wrong but all you need is a 3 core / earth from the main light to the isolator, then 3 core / earth from isolator to fan.
From light: Neutral to N in. Switched Live to L1 in.
Permanent Live to L2 in.

To fan: N out to N of fan. L1 out to switched L on fan.
L2 out to permanent L on fan.
Earths obviously to respective terminals.

Apologies if that's not what you wanted but your post is a bit confusing.
 
Sorry if I'm reading your post wrong but all you need is a 3 core / earth from the main light to the isolator, then 3 core / earth from isolator to fan.
From light: Neutral to N in. Switched Live to L1 in.
Permanent Live to L2 in.

To fan: N out to N of fan. L1 out to switched L on fan.
L2 out to permanent L on fan.
Earths obviously to respective terminals.

Apologies if that's not what you wanted but your post is a bit confusing.
Hi that's what I've got, but not working?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Prestatyn
Business Name
FLS

Thread Information

Title
En suite extractor fan with run on timer
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
Paddington,
Last reply from
Specialist,
Replies
23
Views
2,018

Advert

Back
Top