sivoodoo

Client wants cooker moving and therefore a longer cable run is required, the existing cable tests out fine with >299M ohms and good continuity.
The cable has been run behind old oak panel which client does not want touching, so whats my best option for joining 6mm cable that meets regs?

Thank you
 
every time I have extended a cooker circuit I have just stuck the cables in a 4" adaptable box and used 63 A connectors, All terminations have been accessible and It had a 230 V sticker on it so as far as i am concerned it complies with all regs, but then I am just a trainee so what do I know lol!
 
Client wants cooker moving and therefore a longer cable run is required, the existing cable tests out fine with >299M ohms and good continuity.
The cable has been run behind old oak panel which client does not want touching, so whats my best option for joining 6mm cable that meets regs?

Thank you

hi there
would it be possible to put an isolator there ? done this a few times:)
if i would go with the metal bax and connectors i am not a lover of trough crimping seen quite a few burn outs using this method

the other can you run a new cablef rom else where

cheers
 
tangent
we were using wagos over 10 years ago, suprised its taken as long to become mainstream over here.
i use to do a whole lot of european work and theyve been using them over there for, well for a long time
 

Reply to Extending 6mm cable in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi I am seeking help and best practices to achieve below tasks. I am not across regulations hence will appreciate best approach to achieve below...
Replies
11
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
617
Evening all, Currently 1st fixing new extension however the existing cooker hood duct which was on outside wall will now be part of new utility...
Replies
2
Views
643
Howdy All, just after a 2nd opinion as i'm doubting myself. I went to a property to look at replacing the ccu, I noticed what I thought was a...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock