smithdarr

Hi,

I'm after a bit of advice on fitting a consumer unit to new extension. The existing house C.U is a 6 way Wylex 100A (non-RCD protected with 2 rings and 2 lighting circuits) with two spare ways. I was hoping to use a 63A MCB in one of the spare ways to feed a new C.U(via earthed metal conduit) in the extension which is to be a kitchen/Diner. From the new C.U I am feeding a cooker circuit, ring, lighting x2, heat/smoke detectors and a feed to a shed. However, it seems you can only get a maximum 40A mcbs for single phase boards and I would presume, even with diversity applied this wouldn'nt be large enough to feed a seperate C.U with a cooker circuit and ring etc. I was looking to use a dual 63a RCD board in the extension and the reason that I'm not just replacing the old C.U is that its current location is not very accessible.
P.s There is 63A RCD shower enclosure fed from supply side of the existing C.U.
Any suggestions of a better way of going about this would be much.appreciated.
Cheers.
 
Is it your property or a clients? I would SUGGEST a new board. If it's not accesible to go in the same place what about changing the tails to longer ones and extending the cables to a convenient place? Unfortunately a job like this has so many variables , without seeing it , it's really difficult to offer any definitive advice. If there's anything specific I or anyone else can maybe help with please feel free...
 
I agree, replacing the existing board would be best. Ideally you should run the new circuits back to the exisiting board (once changed) unless it's going to be totally seperate to the rest of the house.
 

Reply to Extension Consumer Unit in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi, The `power went out throughout the house this afternoon but only to the sockets, the lighting circuits are all fine. I went to the consumer...
Replies
9
Views
1K
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
731
As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock