Hi all,

I can't understand why but I always get a small (minimum 0.06mA) earth leakage reading on extension leads (even without surge protection).

Is this normal?

If it is, please could someone explain how earth leakage occurs on a simple extension lead?

Thanks
 
How are you measuring it?

if it is a long lead, there could be some inductive coupling between the cores as they are running parallel to each other
 
This is likely capacitive leakage. For example, one metre cable with 30pF between line and earth conductors would have a capacitive reactance of 1/(2*pi*50*30Exp-12) = approx 100MΩ. At 230V a 25m cable will leak 25*230/1Exp8=0.058mA. This is a genuine current that leaks across all cables all the time they are energised but because it is reactive it doesn't register as power consumption on a watt-hour meter. It's also pretty small, and off the bottom of the scale of some testers; mine only displays <0.1mA when this low.
 
Last edited:
Are tutor taught us all that malarkey and all made sense at the time, as of today its pie to the power of 12 up in the sky..

Excellent that you so fluent.
 

Reply to extension leads - earth leakage in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hi All, My colleague and I are currently doing PAT/ISITEE Testing, and we've hit a snag with a bit of equipment - we've got 19" Racks for our...
Replies
8
Views
394
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
785
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Replies
17
Views
2K
Hi. I've read much about ac vs dc but can't find a 'simple' answer. If current alternates 50 times per second in a uk mains circuit, why do live...
Replies
23
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock