Daljit68

Hi

I’m thinking of changing an extractor fan (in a WC) to one with a run on/timer. The current set up doesn’t have an isolator, and wiring runs from the light bulb to the fan, which is sited in the ceiling about 18” away. The fan is vented through a flat roof above.

Now, I realise that i’ll need a permanent live and to fit an isolator switch. I’m thinking of doing this:
- to leave existing wiring as is, and take a live feed from a lighting circuit junction box in the attic;
- to install an isolator switch in the permanent feed run, ie in the attic.

I’d rather not have to channel into walls to run a new 3 core cable.

Thanks
 
Hi

I’m thinking of changing an extractor fan (in a WC) to one with a run on/timer. The current set up doesn’t have an isolator, and wiring runs from the light bulb to the fan, which is sited in the ceiling about 18” away. The fan is vented through a flat roof above.

Now, I realise that i’ll need a permanent live and to fit an isolator switch. I’m thinking of doing this:
- to leave existing wiring as is, and take a live feed from a lighting circuit junction box in the attic;
- to install an isolator switch in the permanent feed run, ie in the attic.

I’d rather not have to channel into walls to run a new 3 core cable.

Thanks
Sound like a rubbish plan.
 
Do you not think it would be a good idea to isolate the 'switch live' and 'neutral' as well?
 
Last edited:
or give this guy a job.
49903
 
Hi - just so you know - new regulations from January mean that changing the wiring on a circuit with lights will require an RCD be fitted, if it’s not already. And depending on details, a building works notification (Part P) might also be required as you are doing electrical work in a bathroom. An Electrician can help you with both of these aspects, as well as testing the completed works are safe, just saying :) .
 
That really doesn't sound good at all Daljit, also dangerous because:

1. You could be taking the permanent live (PL) from a different circuit.
2. You will only be isolating the PL not the switch live, so if you do use the isolator switch (i use the term lightly) you would still have a live fan when the light switch was on. Someone who moves in after you could well get an electric shock as they would never suspect that it had been wired so badly.

I realise you are probably trying to safe some money but you really should get an electrician to do this work.
 
Hi - just so you know - new regulations from January mean that changing the wiring on a circuit with lights will require an RCD be fitted, if it’s not already. And depending on details, a building works notification (Part P) might also be required as you are doing electrical work in a bathroom. An Electrician can help you with both of these aspects, as well as testing the completed works are safe, just saying :) .
Hi, WC so no special regs
 
That really doesn't sound good at all Daljit, also dangerous because:

1. You could be taking the permanent live (PL) from a different circuit.
2. You will only be isolating the PL not the switch live, so if you do use the isolator switch (i use the term lightly) you would still have a live fan when the light switch was on. Someone who moves in after you could well get an electric shock as they would never suspect that it had been wired so badly.

I realise you are probably trying to safe some money but you really should get an electrician to do this work.
Thanks for considered comment! It’s less about saving cash, it is a simple job but just don’t like the idea of channelling into walls.
 
Hi - just so you know - new regulations from January mean that changing the wiring on a circuit with lights will require an RCD be fitted, if it’s not already. And depending on details, a building works notification (Part P) might also be required as you are doing electrical work in a bathroom. An Electrician can help you with both of these aspects, as well as testing the completed works are safe, just saying :) .
It’s a WC
 