Daljit68
Yes, CU is split rcd, with single 2.5mm T&E cable running (embedded) to wall switch (1m away) then (embedded) to roof void. If this was a 3 core wire instead of T&E I wouldn’t be posting on here ie I wouldn’t have a problem!So there is a switch live wire going to the switch from the light?
There should be a 'permanent live', 'switch live' & 'neutral' at the light then. Can you not tap of these?
Does your CU have an RCD?
So I have Switch L and N. I’ll connect these to a fan isolator switch fixed into ceiling. Then run permanent live from lighting junction box in attic to same switch. That way, single switch will isolate for servicing, complying with regs.