fan iso' inside bathroom

J.C.E

~
Arms
evening chaps

regs and osg at home (will be looking later) but see if I can get an answer before I get home

basically started a full rewire today- but bathrooms recently been renovated and tiles etc- whilst this was done they had fan installed with a 3pole isolator- but this is inside bathroom- behind door which is outside z2.

planned to test new wiring for fan+ isolator and keep- just rewire the center light as part of the rewire.

I know ideally- it should be outside or pullcord (wet fingers etc)

But will I get away with it- being outside z2? or just install new one outside and blank off old 1
 
Outside of zone 2 general rules apply, which means the accessory must be suitable for the environment.
If the switch is not likely to get sprayed with water then it is OK.
Just leave it as it is, there is no "get away with it", it complies with the requirements.
 
wot he said. can't envisage a scenario where a spark will have wet hands if and when he needs to isolate the fan for maintenance.
 
moved it outside anyways today!
muppet that done it has only taken 2 singles down to it through an old 16mm pipe( a sf in from light and a sf out to fan)
 