My rough rule of thumb is if I'm adding/removing circuit cable or splitting existing circuit cable then it's altering the original design of the circuit sufficient to require a cert.I would look at it in this light; if the work I do involves anything that I or the client would class as consumables (bulbs, bit of sleeving, plug top fuse) or a level of preventative maintainance expected of a basic householder then I wouldn't deem a cert required (unless you're including testing), any work that involves replacing or maintaining a fixed wiring fitting the I would generate a cert for - this is meant as a dynamic list -we all know the jobs that would be deemed beyond the realm of joe public - and as such is non-exhaustive, by all mean so add your own;
Bulb change; no cert
Tightening loose switch connections in sockets/switches; no cert - unless testing done beforehand and it flagged suspect loose terminals
Changing plug top fuse; no cert
Changing plug socket/light switch; generate cert (because we're all tightening to manu torque settings aren't we)
Changing light fixture; generate cert
work within CU; generate cert
Feel free to expand on
For such a minor repair I would do the Eicr and right a comment on the observation page stating that the observation was rectified at the time of inspection and write info or note in the column where you would normally but the code
I think there's a bit of confusion as to weather the fault was duscovered during an EICR or as a fault call out.Is an EICR intended/designed to be used for a minor repair?
No but the OP was already doing the Eicr so why caurse confusion issuing an unsatisfactory report and another peace of paper saying you fixed it at the same time.Is an EICR intended/designed to be used for a minor repair?
No but the OP was already doing the Eicr so why caurse confusion issuing an unsatisfactory report and another peace of paper saying you fixed it at the same time.