jjnr78
always split the circuit in half and meggar it, the quickest way IMO, otherwise your chasing ghosts, basic stuff really, I expect a choke or capacitor has melted and shorting out the wires, if the circuit is as large as you say then break it in half.
Thanks for all the help. Perhaps i shouldn't have posted at this stage. i'm very experienced in fault finding and therefore know the usual procedures and what an ordeal it'll be to pull everything apart (heat shrunk joints- not easy) and then put back together. There is no over load issue and the testing has been performed L/N to cpc thus far. We are due to return to site soon, but we are very stretched so i was trying to discover whether high tuff was the wrong choice of cable as it allows an ingress of water. i've seen it with other types and we use rubber pond/ fountain flex. this job looks well put together, so my thoughts were to rule out whether the cable was the culprit. I'll batch a few loads and test across all conductors with the loads disconnected and gauge from there.
i do however appreciate the assistance. cheers