Hi all,

OK, so was sent to a job today for upgrading a kitchen. The existing mains was an older MEM board which the newer Eaton RCBO's wont fit. The only circuits being amended are the kitchen ring main (32 amp) and the lighting circuit (5 amp). The customer would not have been keen on changing out the whole board so I am fitting a new Hager 2 way board (40 amp main RCD switch). There is plenty length on the cables, so am able to pull them into the new board no problem. Rather than taking 16mm tails off of the incoming side to feed the new board, I am going to feed with with a 6mm twin and earth for the supply off of its own MCB in the MEM board. Ideally I would have liked to have the 2 way board run off of a 40 amp MCB but there is now a spare 32amp breaker seeing as I have now moved the kitchen ring into the new 2 way board.

Obviously the kitchen ring will not be pulling near 32 amps, neither will the lighting circuit be pulling near 6amps so when it comes to maximum demand I know I am well clear. As you know the old MEM breakers are not off the shelf items which is why I intend to use the old 32 amp MCB to feed the board.

Has anyone else come across this conundrum in the past? Some may question why a 32amp and 6 amp circuit is being fed from a 32amp MCB.

Would appreciate any comments. I have a tendency to overthink things even when I know they are safe! haha.

Cheers
 
Welcome to the forum :)

The job would surely have been assessed prior to commencement and the customer informed of options, your question/solution here suggests you are playing a design and build method IE .. turning up blind and designing the install as you go along (Not a proffesional approach unless you been dropped in it by higher orders), you suggestions are poor in design in you provides little if any discrimination (not even partial) so why not fit a tails joint box and split the feeds to each board thus maintaining the best discrim' possible of a domestic supply.
 
How old is the MEM board? The wholesalers I use have a fair selection of memshield 2 and 1 era stuff on the shelf
 
As darkwood has suggested, it would be so much better to split the tails using a Henley block. And why not put in a slightly bigger second CU to allow for future expansion, to avoid having to chase down obsolete parts at a later date?

I personally don't like running one board from another via an MCB, here you have the perfect opportunity to avoid doing this.
 
Welcome to the forum :)

The job would surely have been assessed prior to commencement and the customer informed of options, your question/solution here suggests you are playing a design and build method IE .. turning up blind and designing the install as you go along (Not a proffesional approach unless you been dropped in it by higher orders), you suggestions are poor in design in you provides little if any discrimination (not even partial) so why not fit a tails joint box and split the feeds to each board thus maintaining the best discrim' possible of a domestic supply.

Thanks for the responses. I normally would do this with Henley blocks however there are no tails - just the concentric cable coming directly into the main switch all in behind the wall with no wiggle room. Ie all you can see is the board on the wall. It's a block of flats. And yes, we are always dropped in blind and have to do it all from design to installation each time.

To answer the other question on the age of it I'm not sure. However the part number on the MCB is 321qb?


thanks
 
Hi all,

OK, so was sent to a job today for upgrading a kitchen. The existing mains was an older MEM board which the newer Eaton RCBO's wont fit. The only circuits being amended are the kitchen ring main (32 amp) and the lighting circuit (5 amp). The customer would not have been keen on changing out the whole board so I am fitting a new Hager 2 way board (40 amp main RCD switch). There is plenty length on the cables, so am able to pull them into the new board no problem. Rather than taking 16mm tails off of the incoming side to feed the new board, I am going to feed with with a 6mm twin and earth for the supply off of its own MCB in the MEM board. Ideally I would have liked to have the 2 way board run off of a 40 amp MCB but there is now a spare 32amp breaker seeing as I have now moved the kitchen ring into the new 2 way board.

Obviously the kitchen ring will not be pulling near 32 amps, neither will the lighting circuit be pulling near 6amps so when it comes to maximum demand I know I am well clear. As you know the old MEM breakers are not off the shelf items which is why I intend to use the old 32 amp MCB to feed the board.

Has anyone else come across this conundrum in the past? Some may question why a 32amp and 6 amp circuit is being fed from a 32amp MCB.

Would appreciate any comments. I have a tendency to overthink things even when I know they are safe! haha.

Cheers

You could put in a slightly bigger board, and, if its not a really long circuit and the load is not heavily focused on one side of it, split the kitchen ring into 2 20A radials. You'd then achieve the discrimination that you need.
 
The problem is you will never achieve discrimination using an MCB to supply a distribution board but I find installations done this way a lot, if its is explained to the customer the problems that installing the installation this way and they are prepared to put it with then that's up to them , if they don't wish to pay for the CU upgrade then it sounds like its your only choice.
 
Thanks for the responses. I normally would do this with Henley blocks however there are no tails - just the concentric cable coming directly into the main switch all in behind the wall with no wiggle room. Ie all you can see is the board on the wall. It's a block of flats. And yes, we are always dropped in blind and have to do it all from design to installation each time.

To answer the other question on the age of it I'm not sure. However the part number on the MCB is 321qb?


thanks

You didn't google the part number then?
A Google search reveals that it's memshield 1 and that rcbos do exist, it's just a matter of finding them.

8daf88cc8afd952a99ebe49ca65d9c92.jpg
 
hello all again, and thanks for all your replies. I connected up the two way board today, as discussed with the 6mm cable feeding it - it's behind the wall so looks tidy. Have also asked someone in the office to order a 40 amp MEM breaker off of e bay to feed it with so will change out the 32 amp one when it comes in.

To answer some of your replies;

davesparks - i initially called Edmundson Electrical about RCBOs that may have fitted. They explained that that particular type is extremely rare and that Eaton were quoting them (wait for it).....£400 per RCBO?! Yes, we both laughed about it through gritted teeth. In any case, the picture you sent looks like it takes up two spaces so this wouldnt have been feasible.

Flanders - I totally agree. Put yourself in the customers shoes - they had a surveyor out to look at the job and measure up for the kitchen. You cant then turn around to them once the job has started and say (once they have paid) that ideally the fuse box needs upgrading and that will be another £500.

Electric Magic - thanks, but that would not have been practical either.
 
hello all again, and thanks for all your replies. I connected up the two way board today, as discussed with the 6mm cable feeding it - it's behind the wall so looks tidy. Have also asked someone in the office to order a 40 amp MEM breaker off of e bay to feed it with so will change out the 32 amp one when it comes in.

To answer some of your replies;

davesparks - i initially called Edmundson Electrical about RCBOs that may have fitted. They explained that that particular type is extremely rare and that Eaton were quoting them (wait for it).....£400 per RCBO?! Yes, we both laughed about it through gritted teeth. In any case, the picture you sent looks like it takes up two spaces so this wouldnt have been feasible.

Flanders - I totally agree. Put yourself in the customers shoes - they had a surveyor out to look at the job and measure up for the kitchen. You cant then turn around to them once the job has started and say (once they have paid) that ideally the fuse box needs upgrading and that will be another £500.

Electric Magic - thanks, but that would not have been practical either.

The "surveyor" needs to be better trained - or be a sparky.

So you were sent to the job by a kitchen company - were you on a fixed price?
 
The "surveyor" needs to be better trained - or be a sparky.

So you were sent to the job by a kitchen company - were you on a fixed price?
Jesus give the guy a break, the worst thing that will happen is that the customer will have to reset 2 MCB's???
 
Jesus give the guy a break, the worst thing that will happen is that the customer will have to reset 2 MCB's???

There are countless kitchen companies who don't spec the electrics properly and give the work on fixed prices to poor sparks across the country. The OP didn't spec the job, he just got landed in the poo by the kitchen surveyor. I am not blaming the op
 
There are countless kitchen companies who don't spec the electrics properly and give the work on fixed prices to poor sparks across the country. The OP didn't spec the job, he just got landed in the poo by the kitchen surveyor. I am not blaming the op


Haha, wow - this has stirred up some emotions eh? We are actually a very reputable and high end kitchen and bathroom supplier but as far as electrical knowledge, it's only the four electricians who are doing the jobs. Yes we work on a fixed price but if there as issues then they are extras. The surveyors know a little when looking at the jobs but not the same in depth knowledge that us sparks have.

Btw Murdoch, what does OP stand for?

thanks

dave
 