Having gone back and forth through the onsite guide and BYB, am I right that with socket outlets in commercial premises it is the same as domestic 2.5mm and 100m2 ring main and 75m2 for a 4mm radial circuit? So application for diversity would be 32amp for first circuit and then 50% of every circuit thereafter?

Thanks, having a brainless moment!
 
Last edited by a moderator:
Commercial and domestic have the same rules for circuit design, so the advisory information about the maximum square area covered by a ring final circuit on a 32A breaker in 2.5mm² cable (100m²) and a radial final circuit in 4mm² on a 32A breaker (75m²) is the same for both types of installation.

The diversity guidance in the OSG then advise the diversity figures you give (100% of the first standard socket circuit and 50% of the rest).
However it is often a good idea to assess the diversity based on likely usage if at all possible.
 
Commercial and domestic have the same rules for circuit design, so the advisory information about the maximum square area covered by a ring final circuit on a 32A breaker in 2.5mm² cable (100m²) and a radial final circuit in 4mm² on a 32A breaker (75m²) is the same for both types of installation.

The diversity guidance in the OSG then advise the diversity figures you give (100% of the first standard socket circuit and 50% of the rest).
However it is often a good idea to assess the diversity based on likely usage if at all possible.


OP don't call it a ring main, it's a ring final circuit