C
cristafar
Any of you guys know if it is ok to activate a relay using the sounder output of a fire alarm. It's operating a mag lock obviously when the alarm goes off the mag lock breaks. Thanks in advance.
Thanks for all your replies guys. I am currently working for a firealarm company and noticed that the alarm we serviced had a relay that was operating using the sounder output terminals, all the other relays in panel were in use and the 24v aux. so I was just wondering if this was to go down on the certification. The firealarm engineer I was working with seems a little laid back and seemed to think it was ok because it will activate the relay on firealarm activation, but I just don't think it was right still.
Thanks anyway guys
You need to rememebr, that if you use the sounder output to activate the relay and unlock the door, then when the alarm is silenced, by the silence button for any reason, before the evacuate is given, then the mag lock will lock the door, as its a non-latched output, unlike the fire output/relay.
This is a very common arrangement to operate magnetic fire door hold backs!!
Especially on systems that don't have conventional operation layouts!! Projects in the Middle East, have a tendency to get changed because some high manager want's it to work differently!! lol!! And NO, they will then not then conform to any recognised standard, but it still gets done!! lol!!