H
hhhunzai
Hello Everyone!
Refer to the subject, please guide me in a situation, there is a power cable 25sq. mm, 4 core pvc/pvc non swa buried directly in ground and in some ducts.The cable has damaged anywhere and it shows short circuit between every conductor.I have tested with a uni-T multimeter, it shows almost 2 to 3M ohms resistance between each conductor.The operating voltage is 3 phase, 415volt, 50Hz
Please suggest me a technique to sort this short circuit out, without digging the all area and ducts in ground.Is it possible to locate the exact location of the leakage area?
Your opinions are requested in this regard
If your getting 2 or 3million ohms between the conductors, where the hell is your short circuit??
yes your are right, but it shouldn't show this resistance too it should show infinity.
As I am checking this cable with a "Multimeter not with a Megger, With magger I think it will show a lower resistance.
Multimeter has a low voltage and megger test is about 1000Vlots.
Well if it is indeed a short the first thing to do is walk the length of the cable and look for intrusions and disturbances, presuming you know the run .
As I have mentioned in my First post, I want to know a technique, if there is one; to detect the problem without digging the ground. It an underground buried cable, almost 2.5 feet under the ground surface.
Is it possible by energizing the cable and then check with tool, like a meter or something else.
I'd be inclined to insulation test it again using at least 500vdc with a known good and calibrated meter.
A dig-up is rather a big decision to make from the readings off a multimeter !!!
Then why pray are you using a multimeter, when you should be using an insulation tester?? Use the right tool for the Job. You will then KNOW that you have a problem!!!
The only way your going to find a fault on any buried cable is by use of test kit that can see/locate a high resistance point and give you a distance from the testing position. As you don't even have an insulation test kit, i'm pretty sure your not going to have fault location test kit!! So if there are no physical/visual indicators as to where the fault could be, your pretty stuffed i'm afraid!!
I misread your original post, i thought you were referring to a multi function meter!!
You got my point, but I have just a multimeter right now. I am sure enough about what I am saying. I have performed such test before and the problem was cable insulation leakage, not complete short but due to moisture and a minor leakage in cable this make breakers to trip.
So the point is, Is it possible to detect this leakage with a tool, I think there should be?
Sorry had to go, if you walk the length you may be able to see where the damage has occurred . You could hire a Cat and Genny or a Wheatstone bridge to find the fault if you have one.
I will make it by myself, I have the idea about this bridge, just tell me how I can perform test with Wheatstone bridge.
http://www.ceh.org.uk/docs/manual/O20001.pdf
I have included the user instructions for the Cat/ Genny and the Wheatstone bridge. The Cat and Genny should be the easiest for you as it has a signal generator.
The Wheatstone bridge is easier to use if at least one of the cores are intact. Simplified it measures the resistance equally along the length of the cable using either one of the intact cores or a separate cable connected to the suspect core. the readings are calculated as per the chart supplied with the tester and should be accurate for about a metre. Forgive me if I have got it wrong Lads it's been a long time.
With 3MΏ at 415 V I’d be inclined to just switch it back in to service. If it holds then OK, if it blows you will have a better (lower) fault reading. You really can’t do fault finding of this type with a multi meter. As to the Wheatstone bridge 3MΏ is to high for it to work.
Four core Power Cable Short Circuit
Australia
hhhunzai,
Knobhead,