Do check there is an earth rod and that there is an earth conductor connected to it. Another thing for the electrician to check. If soil looks dry pour a few gallons of water around it.
See page 10/28: I know this is not the RCD fitted in your CU - I cannot find any detailed information on line - but if it is similar to the one on 10/28 then the Contact Position Indicator (CPI) should change colour from red to green when the contacts open on trip. That you do not see this happen nor the blue toggle lever move is very odd and suggests it is faulty. However, I cannot establish for certain whether on trip the blue toggle should flip to the off(0) position. Others might know the detail of ABB RCD operation.
on some of them the toggle may not move from the on position but the internal part will (you would feel free movement between the on position and half way to off position) sometimes it make you think its broken. but they usually have some type of indicator window on them.
still they have to be switched completely off before they can be reset.
ABB units are notorious in France for being of the lowest quality and going AWOL, change it to a Hagar or Legrand, or even Siemens, Legrand are available in any of the Brico sheds.
And just in case someone reading this does not know, the protective conductors of the various circuits must have a cross section equivalent to the conductors in the distributed circuit i.e. no UK T&E, there is also a requirement for all cables to be double insulated, so all must run in plastic conduit (gaine) there are circumstance's where metal conduit can be used, but again special protection has to be in place. Oh yes all MCB's have to be dual pole and have a minimum air gap of 3mm on disconnection this precludes most MCBO's I believe.