This is a reply I gave on a previous thread :-
In reply to the op it is possible to achieve fan isolation of all lives, fusing of both lines and have the bathroom light unaffected by fan isolation using just a dp sfcu and a dp light switch. The wiring is a bit 'busy'.
Supply into dp switch, two x two core cables to sfcu and one x three core from sfcu to fan. Connect as follows :- Supply l to dp light sw S1, n to wago in light sw back box. Using one of the two cores cables, light sw S1 to sfcu l supply, sfcu l load back to light sw S2. Second two core, light sw L2 to wago in sfcu back box, n from light sw wago to sfcu supply n. 3 core is connected to sfcu l load, sfcu n load and switched line to sfcu wago. The light is connected to dp light sw L1 and n to light sw n wago.
Description looks confusing but draw it out.
 

Attachments

  • image.jpg
    image.jpg
    132.7 KB · Views: 164
Last edited by a moderator:
This is a reply I gave on a previous thread :-
In reply to the op it is possible to achieve fan isolation of all lives, fusing of both lines and have the bathroom light unaffected by fan isolation using just a dp sfcu and a dp light switch. The wiring is a bit 'busy'.
Supply into dp switch, two x two core cables to sfcu and one x three core from sfcu to fan. Connect as follows :- Supply l to dp light sw S1, n to wago in light sw back box. Using one of the two cores cables, light sw S1 to sfcu l supply, sfcu l load back to light sw S2. Second two core, light sw L2 to wago in sfcu back box, n from light sw wago to sfcu supply n. 3 core is connected to sfcu l load, sfcu n load and switched line to sfcu wago. The light is connected to dp light sw L1 and n to light sw n wago.
Description looks confusing but draw it out.
Like this?
Extract fan and light DP switch and SFCU.jpg
 
Yes that makes sense, the only thing is if you wanted to do it from a pull cord you would need to use a double pole one not just your ordinary type.

im just thinking about this layout as have a couple of extensions I'm working on so might just reconfigure it slightly to work this way.

i know it's obvious in a way but thanks for sharing it.
 
Last edited by a moderator:
we fit 3amp circuit breakers for bathrooms normally get 2 from one, this helps split lighting circuit up also, if we have multiple bathrooms en-suites utilities ect then we grid switch from 6-10amp circuit breakers.
 