1. Jacko: None of us have a problem with you being an apprentice, we've all been there.
  2. When you ask a question, please give all relevant information it makes it easier for us to give you the right answers.
  3. My best advice at this point would be, tell your friend to call in a proper electrical company to look at it.
  4. Don't use what's been installed until all problems are sorted and it's been properly tested / certified.
 
Have you or you or your friend any idea how to contact this idiot, I would suggest you get him back to disconnect this mess and leave it to someone who knows what they are doing. This Muppet has not even taken Volt drop, installation method, or loading into account, in my opinion the whole install wants redesigning, how much did your friend get taken for? I'm sure Sparkychick wont mind but She is from Wales and maybe can take a look if it's not too far to travel. Good luck, do you have access to the Trainee section? well worth you applying, one of the Staff should be able to help you in that area, give it a go plenty of free advice, with no mickey taking, or abuse.
 
Thanks for all the advice. It's been a great help. I will be calling there later on today to give him the news.

Just for my own education and I have been looking up a few things before I posted on here...

1. Would you have to make the board in the garage a TT system and only take a live and neutral supply down? (I read that somewhere)

2. Am I right in saying that you could Have this circuit supplied off a 2.5 swa cable from a 20amp breaker in the original db if that is rcd protected? The board in the shed with have its own EDC and two circuits, one 6a for lights and one 16/20a for the 1 x double socket.
 
Thanks for all the advice. It's been a great help. I will be calling there later on today to give him the news.

Just for my own education and I have been looking up a few things before I posted on here...

1. Would you have to make the board in the garage a TT system and only take a live and neutral supply down? (I read that somewhere)

2. Am I right in saying that you could Have this circuit supplied off a 2.5 swa cable from a 20amp breaker in the original db if that is rcd protected? The board in the shed with have its own EDC and two circuits, one 6a for lights and one 16/20a for the 1 x double socket.
Why would you want to spur off of the RFC in the house and put a CU in the shed? bad practice, imo,
 
Hi Jacko: Not trying to be picky, but is it a shed or garage? You've used both descriptions.
In domestic it's called a Consumer unit or CU not a DB.
 
whaere in wales? one of us may be close to you.
 
from a MCB in the CU (DB). SWA to shed. RCD garage CU with a 16A and a 6A MCB. if there are extraneous metal parts in shed, then that would complicate the issue as regards bonding if PME earthing applies.
 
What size swa would be suitable? I'm guessing it depends on load?

In this case where we only have 1 double socket and 1 pendant?
 
I was assuming in advance that the OP may, I say may spur off the ring, wrong in this case, probably down to old age and one beer to many. Best to ignor my previous OP sorry.

No worries mate, thought I was losing it.
Mind you with some of the threads lately, it's enough to make us all lose it.
Save some beer for me & tel mate, think we need it :D
 