Discuss Garage Supply Made In to TT system.. why ?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
T
TPES
Hello
It would be interesting for some to know what situation you need to make a garage supply a TT system.
An explanation and the theory as to why this needs to be done would be helpful to many students.
It may be an obvious answer to many but it’s the simple questions many won’t ask as they think it makes them look stupid.
Ha ha.
Im not giving you my thoughts... i'll have you all in stitches!! :D
Im not 100% sure...
Go on then.. hit me with it?
http://www.iee.org/Publish/WireRegs/...s_answered.pdf
copy and pasted
Exported earth..
here goes; basics first..
Why do we use "earth at all"?
There is protective & functional earthing.
protective earthing comprises source & electrical equipment earthing.
[functional earthing is for stuff like IT equipment with high leakage currents...but we will ignore them for today!]
quote from NICEIC..
"The purposes of source earthing are:
• To preserve the security of the supply network by limiting the potential of the live conductors (with respect to that of Earth) to a value consistent with their insulation.
• In the case of a TT system, to provide a path for earth fault current and protective conductor current to return to the source of energy via Earth. Without this path, devices for protection against electric shock and fault current to earth will not operate. "
equipment earthing is joinin all of our metal bits etc.. together! {exposed conductive parts joined to MET} create our EEBADS zone.
In the event of a fault a path must be present for all of them nasty electrics to make there way back home to their source.. through a circuit (i.e. the earth fault loop path) and provide a means to cut off the supply!
The earth fault loop path (Zs) must be a low enough resistance to cause the circuit breaker (MCB or fuse) to trip within the required safe operating time. {5sec 0.4sec?}
With a longer circuit, e.g. remote garage bottom of the garden, the Zs may be to high. unless you put in some bigger CSA cables.. simple solution can be to make garage a TT installation .
You are permitted in the wiring regs to join the TT rod & MET together.. BUT if you do.. "All of the CPC's must be capable of carrying the max PFC for any part of the installation" because for example.. a fault in the shower on the house.. could make a path down to the earth rod in the garage! So unless you go back to stickin in mega big CPC cables... the way to stop house fault currents going through the garage is to keep both earth arrangements separate! (542.1.8) The earth of the SWA is protected back to the house.. but no further forward to the garage.
Keepin the above bits in mind.. we need to also consider potential difference..
If you have 4 equal resistors across a supply.. they acts as a potential divider splitting the supply voltage into quarters if you put a meter across each resistor!
A long earth path is a potential divider to any earth fault voltage..
nearest the source it is closer to zero.. further along the wire with reference to the source the voltage increases..
If you have simultaneously accessible "near earth potential" conductors, during a fault, you would need to be absolutely sure no fatal voltage induced current could flow through somebody grabbing hold of both earths.
With our garage we have a local earth rod..
and the house MET potential could be 'exported' out to the vicinity of the garage via the SWA protection...
The SWA must be protected... but this protection must NOT be accessible to Joe Public leaning up his metal clad garage fitting..
He should ONLY have contact with the garage earth rod potential..
Unless of course you have baco-foiled the whole of the garden to ensure the mass of earth around the house is all at the same potential???
This is taken from else were , but covers the basics quite well
HTH
__________________
Absolute bull****, if the supply is tns, no need for further protection..unless of course you supply in twin, no earth... then you need to provide an earth point. It is basic simple, no problem it costs nothing, 5 quid for an earth spike? What are you on?
I don't get it, what is the argument? save 5/10 quid?
Its generally thought that if the garage has services (water etc) then a TT system in there would prevent you from having to run a separate 10mm main bond to it from the MET in the house.
There are also some schools of thought that if you export the PME and the neutral/earth became disconnected (underground in street) then you have lost your earth return from the garage, whilst the main bonding to services in the house would act as a temp rod.
It is the DNO's that generally dont allow the export of PME.
Hi
also could be worth TT the garage so when fault occurs in garage, it doesn't cut out house only garage trip keep it local, avoid unneccesary disconnection of circuits
To be honest....if your earth loop impedance (Zs) value is low enough,i think it is totally acceptable to extend your earthing system to an outbuilding.I actually prefer to extend off the existing earthing system.
Both systems are acceptable but i wouldnt join the two..
On the other hand as Jason mentioned...if the outbuilding has a water supply then i would make this a TT system and seperate the two earthing systems at or near the outbuilding CU....(end of SWA supply cable for example)
Over the years i have had this conversation with lots of Electrians about outbuildings and they all have different opinions?
just noticed...i spelt electricians wrong!:p
Hello
I can see only 2 reasons why you would want to make a garage supply TT
One) there is no ditribitor earth facility provided
Two) the supply is TN-C-S and the garage is outside the main equipotential zone and can not be made a seperate zone
In the first instance its a simple case of installing a 30ma rcd and electrode and in the secon d the same but ensuring segregation of TN-C-S to the garage eg a sub main
Reply to Garage Supply Made In to TT system.. why ?? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...