Don't we have to be able to isolate all of the live conductors in a TT because because neutral could well be at a higher potential than earth (as the earth and neutral are not tied together)?

That means a double pole isolator is needed.

Thought there is a reg on this, somewhere.
They are single pole switched neutral so in the event of the RCBO being operated it disconnects the live conductors (both line and neutral). The difference between single pole switched neutral and double pole being a double pole RCBO would have overcurrent protection in both poles.
 
Thanks, I missed the switched neutral bit!
I've never come across SBS, where do you buy them? Got a link?

Hi mate, sent you a PM with the details.