Today we got our Hager meter kit for one of their 125A TPN boards. It has a little DIN rail fuse holder as the meter is powered right off the incoming isolator/RCD/etc without any MCB for protection (so the meter can't be switched off without everything going off, presumably so you don't cheat on any internal billing but that means).

So I opened it up to look at the fuses and was rather shocked to see a 0.5A glass LRC fuse! You know, the sort with a breaking capacity of 35A at 250V AC! This is off a 400V TPN board that could have a 10kA fault current at that point FFS!

Even replacing the fuse with a 20x5mm HRC fuse is only good to 1.5kA fault rating. What were the product designers thinking?!
 
Type-tested assembly...the fuse shatters but the box keeps the debris contained?
The meter protects the fuse?
Design specified HRC but stores had run out?
Counterfeit switchgear, meter module actually just contains sawdust?

Dunno, sounds carp anyway.
 
LOL it would probably all arc together across the fuse holders if there was a serous fault in the meter module, you could test it out to see what happens? Slydlok FTW!
 
On a similar theme, one well known gas boiler (cant remember which) used to have a fuse on both the line and neutral incoming connections. Could never work out why they thought that was a good idea.
 

Reply to Hager meter kit fusing stupidity in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K
https://www.linkedin.com/pulse/can-you-really-test-circuit-6-dan-jackson-fiet incasee u dont use liked in heres the article in 2 posts An...
Replies
7
Views
1K
R
Hi all, I got given a past exam paper from the 2391 course tutor however it doesnt come with any answers so I thought id put the question and my...
Replies
34
Views
20K
Flakey
F

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock