alitech

I have recently bought a 10ft pool with an electric filter and heater. Its an intex brand. I have a garden power reel that I use for the lawn bower and strimmer etc which works fine, but its not performing too well on this heater and filter pump situation. The whole reel heats up a lot and the thermal switch cuts off every 30 mins or so. I am using an RCD with this as well.

The pool heater is 3Kw and comes with its own RCD attached. I have read that the heater doesnt need to be hard wired because its 3Kw, hence the use of the extension. Obviously, the extension reel is not cutting it.

Are there any idea on what sort of extension cable I should be using to power these 2 devices near my pool? the other thing I was thinking was that it would be good if there can be a waterproof plastic housing for the sockets as its going to be in the garden and is prone to some water now and then.

Any ideas much appreciated.
 
The best way would be to get an electrician to install some proper external socket outlets where you need them.

Water and electricity can be a dangerous mix which is why there are parts of the electrical regulations dedicated to swimming pools.
 
Thanks noted. Although I do think that my kit doesn't need hard wiring. Are there no extension leads that may do the job?
 
Sounds basic.....but are you uncoiling the whole of the extension lead, or only uncoiling half the reel.....?
 
Then there is an inductance in the reel..........you must uncoil the whole extension reel to feed 3kw or it will just melt
 
Ok sure. I will give that a try. Should I be considering a better heavy duty extension though?
 
You should be following basic rules.......any extension reel must be fully unwound on supplying any load
 
You hope it works....I`m shocked you still have an extension lead left, most would be molten plastic under 3kw load
 
You should also check the rating of your extension lead many of them are only designed to take 10A and have a thinner cable, but the fuses are often replaced with 13A.
At the very least your extension should be rated to 13A and have a 1.5mm² cross sectional area of the wires in the cable.
A dedicated outside socket more than 2.5m away from the pool would be a better idea.
 
Richard what about unwinding the extension lead fully....???
I believe you may have mentioned that earlier!
Obviously that is a requirement and the extension is probably already damaged, but if it is only 0.75mm² flex unwinding it will not help in the long term only the short term.
 
Thanks for helping out guys. Can you guys recommended an extension lead for me please? Hard to find them. Tried most of the keywords on Google
 
I am familiar with these pool setups having had to repair the aftermath of having them plugged in to a 13A socket.
What it comes down to is that a 3kW load with this load profile is too much for a 13A socket. Plus one was rated 3kW at 230V so actually pulled more than 3kW at our actual voltage of ~250V
 