My own problem is that when the grill is on, sometimes the mains trips which takes out all of the other units like boiler freezer etc. The individual trip for the cooker does not drop out! Does that mean there is a short somewhere?
I suspect the switch for the grill as yesterday I turned it a bit when it was on and then the mains did drop out. It doesn't always do that so it seems that there is something wrong with the switch...maybe. I checked one element and the wires to it are fine and it all heats up fine too.
I checked the mains switch on the wall and tightened all the connections, nothing loose or blackened there. I've not checked the back of the cooker yet.
Getting to this switch is going to take a strip down I think so I'd really like to know if that may be the problem.
Many thanks
 
Most likely the grill element shorting to earth I have had them where they work for a bit but as they heat up the short gets bigger and also had one that used to trip as you turned it off, need to get someone with a insulation tester to check it out for you
 
I'm guessing what is tripping is an RCD - either for the whole house supply, or for some circuits. Perhaps post a photo of the consumer unit / fuse box if you can.

If this is the case, then often this is due to earth leakage, e.g. a faulty element or other component. Switches themselves can also be faulty. Ideally get the appliance tested first before changing any random components in the hope that might fix the issue.
 
Most likely the grill element shorting to earth I have had them where they work for a bit but as they heat up the short gets bigger and also had one that used to trip as you turned it off, need to get someone with a insulation tester to check it out for you
Thanks Ian... That sounds very similar. I'll get someone in.
[automerge]1598184391[/automerge]
I'm guessing what is tripping is an RCD - either for the whole house supply, or for some circuits. Perhaps post a photo of the consumer unit / fuse box if you can.

If this is the case, then often this is due to earth leakage, e.g. a faulty element or other component. Switches themselves can also be faulty. Ideally get the appliance tested first before changing any random components in the hope that might fix the issue.
Thanks SJD .
my elec panel small image.jpg
attached is a pic of my consumer unit. The centre switch drops out but not the one on the cooker. I lose all power to the right of that switch of course.
 
Last edited:
if you mean the 2 module device with the RCD sticker under, that covers all circuits to it's right. it means that you have an earth leakage >30mA , presumably on the cooker, but not guaranteed).
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Weston super Mare
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Hello. I saw a question related to the Rangemaster Kitchener 90
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
fred E,
Last reply from
fred E,
Replies
7
Views
958

Advert

Back
Top