Isaac k

EF Member
Messages
6
Location
Glasgow
Hi everyone,

I just had my distributer box upgraded to an RCD box, and I was wondering if anyone could advise me on the quality of the work done here. I know that changing these boxes is a nightmare to do, and truth be told our wiring was a mess before, but for the price we payed I don't believe there should be electrical tape and exposed wires coming out of the box. Also you can see the housing for the old night electricity box which they have decided to leave and they also chose not to cover the channel with all the exposed wires. I'm just curious to see what this forum's take is on this work, and if it was worth the £700 I payed for it.

Thanks!

(This is my first post, so if I am in the wrong category I apologise)
20181022_110122.jpg

20181022_110103.jpg
 

SparkyChick

Making a banana smoothy for my fave gorilla
Staff member
Moderator
Messages
3,694
Location
South Wales
Only a few words...

Shockingly bad, truly shocking.

Have you paid the person who did this? If not, do not until it is finished to an acceptable standard which that is not!
 

SparkyChick

Making a banana smoothy for my fave gorilla
Staff member
Moderator
Messages
3,694
Location
South Wales
Just read the price... holy cow! I'd have been more like £350 to change a consumer unit (that's 1 day plus materials and the assumption there were no other things that needed attention).

As I say.. have you paid them?

Have you got any paperwork from them in the form of an Electrical Installation Certificate?
 

Pete999

Forum Mentor
Messages
21,803
Location
Northampton
Only a few words...

Shockingly bad, truly shocking.

Have you paid the person who did this? If not, do not until it is finished to an acceptable standard which that is not!
Totally agree with SC on this, a total cowboy lash up, hope you haven't paid this bloke yet, although by the tone of post you already have, any certificates issued? was the Herbert who did this registered with any Competent Persons Scheme, NICEIC, NAPIT, ELECSA, STROMA to name a few?
 
Last edited:
OP
I

Isaac k

EF Member
Messages
6
Location
Glasgow
Just read the price... holy cow! I'd have been more like £350 to change a consumer unit (that's 1 day plus materials and the assumption there were no other things that needed attention).

As I say.. have you paid them?

Have you got any paperwork from them in the form of an Electrical Installation Certificate?
Hi, thanks for replying!
No, I have not paid yet as I was fairly confident that this was not good work. The electrition that did the work was self employed and did not issue any sort of paperwork. Any advice on where to go from here?
Thanks for replying!
 

telectrix

Scouser and Proud.
Respected Member
Messages
60,292
Location
cheshire/staffordshire
as you have not paid as yet, then do not pay anything. get another sparks to check it over and give you a price to put it right, and estimate on what the job should have cost. then you have a good standpoint to argue with original spark. tbh, that abortion is worse than even a plumber would do.
 

SparkyChick

Making a banana smoothy for my fave gorilla
Staff member
Moderator
Messages
3,694
Location
South Wales
Hi, thanks for replying!
No, I have not paid yet as I was fairly confident that this was not good work. The electrition that did the work was self employed and did not issue any sort of paperwork. Any advice on where to go from here?
Thanks for replying!
For the record... it was not an electrician who did this. It was a chancer who think's he 'can do electrics'.

Do not pay him, @telectrix is spot on, and I would possibly consider reporting him to trading standards as he should not be allowed to do this anywhere else.
 

Pete999

Forum Mentor
Messages
21,803
Location
Northampton
Hi, thanks for replying!
No, I have not paid yet as I was fairly confident that this was not good work. The electrition that did the work was self employed and did not issue any sort of paperwork. Any advice on where to go from here?
Thanks for replying!
For one don't pay him, is there any way you can check out his registration, did he use a Van or did he use a private car, if a van was used did it have any decals on it saying if he was a member of any Scheme? if he isn't registered I guess your only option would be to go to Trading Standards and take advice from them, good jo you haven't paid up, if you speak to him, ask for an Electrical Installation Certificate EIC (as sparkychick mentioned) as technically the job isn't finished until a cert is issued, good luck, and sorry, welcome to the forum.
 
OP
I

Isaac k

EF Member
Messages
6
Location
Glasgow
@Pete999

He is the owner of his company and I recall him saying he is not a member of any scheme. He told me that in Scotland it is not required. I also just looked at his website and it seems to have good reviews, but I don't see any badge or anything.
 

Pete999

Forum Mentor
Messages
21,803
Location
Northampton
@Pete999

He is the owner of his company and I recall him saying he is not a member of any scheme. He told me that in Scotland it is not required. I also just looked at his website and it seems to have good reviews, but I don't see any badge or anything.
Thanks, the Trading Standards will be your best bet Issac, good luck please if you can let us know the outcome, can you give us a link to his web page?
 

telectrix

Scouser and Proud.
Respected Member
Messages
60,292
Location
cheshire/staffordshire
reviews may be from his wife/girlfriend/
@Pete999

He is the owner of his company and I recall him saying he is not a member of any scheme. He told me that in Scotland it is not required. I also just looked at his website and it seems to have good reviews, but I don't see any badge or anything.
reviws mean nowt could be from wife/girlfriend/boyfriend/rab.c nesbitt.
 

telectrix

Scouser and Proud.
Respected Member
Messages
60,292
Location
cheshire/staffordshire
unfortunately, being an avid viewer of Aircrash Investigation, i will not fly in an aluminium coffin where some spotty young boil in the bag airline pilot sits up front. if i was piloting the contraption, at least if it crashed, it would be my own fault.
 

MFS Electrical

Forum Mentor
Messages
1,152
Location
Scotland, Inverclyde, Greenock
Hi, thanks for replying!
No, I have not paid yet as I was fairly confident that this was not good work. The electrition that did the work was self employed and did not issue any sort of paperwork. Any advice on where to go from here?
Thanks for replying!
Tell him to either get his butt back and sort it or get someone else to sort it and pay him for the materials only
 

DPG

Respected Member
Messages
5,204
Location
S Yorkshire
Amazingly bad work. And some of it wouldn't have been that hard to do properly from the looks of it.
 

GBDamo

Subscribed Member
Messages
840
Location
UK
Hi everyone,

I just had my distributer box upgraded to an RCD box, and I was wondering if anyone could advise me on the quality of the work done here. I know that changing these boxes is a nightmare to do, and truth be told our wiring was a mess before, but for the price we payed I don't believe there should be electrical tape and exposed wires coming out of the box. Also you can see the housing for the old night electricity box which they have decided to leave and they also chose not to cover the channel with all the exposed wires. I'm just curious to see what this forum's take is on this work, and if it was worth the £700 I payed for it.

Thanks!

(This is my first post, so if I am in the wrong category I apologise)
View attachment 45054

View attachment 45055
Is that supposed to be finished?
 

Upton Sparks

Regular EF Member
Messages
65
Location
London
Wow, I've seen worse but that does make the hall of shame alright..


It’s not up to standard but you’ve got that already, first of all did you get a written quotation for the work ?. find out if he’s registered , ask him if it’s not obvious on his website. (most likely not), I'm sure in Scotland you need to do something similar to Part P of the building regulations( which requires notification to building control in England and wales) ,

Contractually he has offered to do some work for you. It’s not up to a competent standard of workmanship, but legally you have to be reasonable about it and give him the opportunity to correct his work. if he’s not registered as A competent person in Scotland, then I don't think you have any worries, as he’s very unlikely to take you to court to enforce a contract he could not legally fulfil.

do look for a second local electrician to check over his work and quote for repairs.

Your entitled to have the job completed to a fit and proper standard of workmanship and it goes without saying it should be safe as well.

as for the price, it does seem quite steep, but that's not really a point, the price is negotiated at the begin of the quotations, if your happy with it then you accept the quotation, or get 3 different quotations is always good ... we all value ourselves differently, and we have different geographic.

I'm not that familiar with the requirements of Scotland for domestic
electrical work. you can check below for more information.

Guidance on electrical work not requiring a warrant (Domestic) - https://www.gov.scot/Topics/Built-Environment/Building/Building-standards/publications/glf2
 

Gazthesparky

Electrician's Arms
Messages
323
Location
Glasgow
Wow that’s Shocking that’s certainly not been done by an electrician total chancer alright.

Yep up here in scotland you don’t have to be registered with a scheme but you certainly should have paperwork and test certificates.

For that price I would have stripped the whole cupboard, new backing board brand new board all labels and stickered up with certificates to boot
 

Murdoch

Regular EF Member
Messages
25,126
Location
Woking
Scheme membership aside ........... ALL fuseboard changes should include a full test of the installation and an EIC be issued to the homeowner ..................

If you get an EIC, could you post a copy on here (your and his info redacted)?
 

shaun1

Regular EF Member
Messages
248
Location
United Kingdom
Were you there when the work was done? The electrician should have spent a good couple of hours (if not longer) going round the entire house carrying out out tests on all sockets and the light fittings/switches. Any idea if any of that happened?
 

telectrix

Scouser and Proud.
Respected Member
Messages
60,292
Location
cheshire/staffordshire
Were you there when the work was done? The electrician should have spent a good couple of hours (if not longer) going round the entire house carrying out out tests on all sockets and the light fittings/switches. Any idea if any of that happened?
pigs flying comes to mind.
 
  • Like
Reactions: DPG

markc123

Forum Mentor
Messages
3,605
Location
Yorkshire.
1) Do not pay a penny, that’s a disgrace.

2) If the Cowboy gets argumentative report him to trading standards for doing work well out of his capabilities. Also, link him to this thread on this forum and inpaticular the paragraph below

STOP! You absolute <insert word> You’re completely out of your depth and are doing work that has the potential to cause harm to persons or properties. Go to college, start again.
 

Deuce

Regular EF Member
Messages
464
Location
Stamford
Crikey - that's so bad I'm angry.

No one who's ever spent a few minutes looking at their own CU would think that was the right way do it. I can't see how it's possible the person that did this is qualified, or in fact even trained at all.

I think someone else said you should get another spark to review the work, and then negotiate with the first guy. I'd be firmer though, as he has provided you absolutely nothing of value at all. It's just dangerous and a mess you now have to find someone else to clear up. If he supplied the CU itself then tell him you'll leave it outside for him to collect once a professional has fitted a new one.

I was about to ask if you could take the cover off and provide a photo of the artistry no doubt hidden away in there... But frankly, I don't want to encourage you to go near it until it's sorted.

In fact really don't take it off. I opened one up once to investigate a failed MCB and then realised that one of the screws holding the cover on had cut through a messily routed circuit live. Those are the sort of hidden dangers that cowboys create without even understanding the danger. I also discovered that the MCB hadn't been remotely tightened on to the busbar, which had led to it arcing, then overheating the busbar to the point it had melted the back of the MCB completely. So whoever put it in had essentially created a fire risk and hidden it behind a booby-trapped cover!! :mad:
 

MFS Electrical

Forum Mentor
Messages
1,152
Location
Scotland, Inverclyde, Greenock
Crikey - that's so bad I'm angry.

No one who's ever spent a few minutes looking at their own CU would think that was the right way do it. I can't see how it's possible the person that did this is qualified, or in fact even trained at all.

I think someone else said you should get another spark to review the work, and then negotiate with the first guy. I'd be firmer though, as he has provided you absolutely nothing of value at all. It's just dangerous and a mess you now have to find someone else to clear up. If he supplied the CU itself then tell him you'll leave it outside for him to collect once a professional has fitted a new one.

I was about to ask if you could take the cover off and provide a photo of the artistry no doubt hidden away in there... But frankly, I don't want to encourage you to go near it until it's sorted.

In fact really don't take it off. I opened one up once to investigate a failed MCB and then realised that one of the screws holding the cover on had cut through a messily routed circuit live. Those are the sort of hidden dangers that cowboys create without even understanding the danger. I also discovered that the MCB hadn't been remotely tightened on to the busbar, which had led to it arcing, then overheating the busbar to the point it had melted the back of the MCB completely. So whoever put it in had essentially created a fire risk and hidden it behind a booby-trapped cover!! :mad:
Did the homeowner/tenant have good life insurance sounds more like an assassination attempt than a CU install
 