Oh dear,… As you mentioned it’s the loft above this ‘Pull Cord’ ISO then id certainly suggest getting above the pull cord and fitting a suitable 40/45amp JB and run a new T&E.Hi,
The shower pull chord switch has snapped at my mom’s home and having unscrewed the switch I discovered a horror show(see pic). So I’ve had cut the wires back to clean them up but having done so it’s left me with nothing reasonable to wire up the new switch.
There’s nothing left on the cable to pull through and access to the loft in this very old dwelling is going to be an epic so re-routing isn’t really on the table.
Could I use some SpliceLine in-line wire connectors to extend the wires and if so would the 32 amp ones cut it?
Any advice would be greatly appreciated, thanks in advance.
I fully commend my colleague who suggested cutting out and fitting a dry liner.
But as this an ‘Isolator Pull Cord’. I could imagine that within a number of operational pulls those feeble plastic wings will give way.???

If however the cables are routing down next to a joint then ‘Jog On’, cut and fit a dry liner, multi- tool out a bit of the joist above and as well as the plastic wings, also screw up into the remaining joist.
Hope this helps.