Well, for the microwave, it has a 2.5mm 1m flex tail pre-cabled so can't change this anyway.

If the concern is that the 32A MCB is not going to protect the 2.5mm cable then surely you would have another problem with the Oven wiring itself e.g I can see that the onward internal wiring from the connection plate of the oven is at most 2.5mm. So if my 2.5mm cable isn't protected, the oven wiring certainly isn't either. Therefore on that basis I can't see any advantage to change my connection tails to 4mm.
 
So the manufacturers instructions are just being ignored?

Only if they are obviously referring to European type regulations, .....and remember European plug tops and wall accessories do not include fuses!! Yet another reason why chopping a moulded fused plug top from an appliances lead/cord can't and won't void any manufacturer's warranty, no matter what the service company say's, if it is then connected to the mains supply in accordance/compliance with BS7671!!

The big problem with multi national manufacturers instructions, is that rarely do they fully relate to countries outside of the appliances country of origin. Look carefully and you will usually see some form of small print, stating that appliance must be connected to a mains supply in accordance with your countries recognised codes/regulations!!!
 