i=p/u
That's If there is an internals fuse .
That's If there is an internals fuse .
So you'd be happy connecting 2x 2.5mm cables to 6mm . What's that reg in brief tel.
So is overload not a problem in op scenario . 2.5 joined with 6mm on 32A breaker .
And would your answer change if inductive load
Appreciate all the responses, so telectrix are you of the same opinion as engineer54 in that a local enclosure in the kitchen is overkill and all that's required is a 32A MCB feeding both appliances with local switch isolation. I also spoke to Neff who said there are no internal fuses within the appliance themselves.briefly, a fixed load is not likely to overload a cable. the only time would be a short circuit, in which case the MCB in the CU provides s/c protection but not overload protection.
Appreciate all the responses, so telectrix are you of the same opinion as engineer54 in that a local enclosure in the kitchen is overkill and all that's required is a 32A MCB feeding both appliances with local switch isolation. I also spoke to Neff who said there are no internal fuses within the appliance themselves.