If that's the main incoming head (no reason to think otherwise) then it must be a TT, surely? There's no earth from the DNO unless for some reason they've split it upstream and delivered it elsewhere (highly unlikely).
) shall I do a Ze test from that earth block to each phase to obtain highest values? Testing the units is straight forward, continuity cpc, polarity, r1 r2 etc I'm comfortable with that. Does that have a different cert?? CheersThe council have been round and done inspections on building work etc now waiting for certs.
No the Ze will be included at the start of your cert. All test results you will include on a common cert.
Yes record highest value. For a TT your looking for a result under 200 ohms